Floor drain by overhead door?????

pletzer28

Member
Joined
Feb 14, 2012
Messages
15
I am in the process of putting up my commercial building for a woodworking shop. Iam wondering i am i required to put a drain by each overhead door? I am located in WI. My shop floor has a 10' x 14' overhead door and i need that floor space level. I have a catch basin by other 10 x 10. which is separated by a wall to the other overhead door. Shop is 2640 sq ft.

Thanks
 
Section 412 of the ICC Plumbing Code does not list any required location near an overhead door. Is it adopted in WI?
 
I don't know of any requirement that would make you put one there unless it's something local. If you are required to put one they are you could always install one of the preformed trench drains along the door line. That would allow you to keep the level floor you want, I'm assuming so you can do assemblies much easier.
 