Then OP stated it was unconditioned space which means it will require a dry system which will cost a lot more than just extending the wet system.
a few sidewalls thru the wall, never hurt anyone
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Then OP stated it was unconditioned space which means it will require a dry system which will cost a lot more than just extending the wet system.
at first, i didn't agree with the other interpretations but now i do and the storage space will be sprinklered. the added cost is not a lot for the scope of the project. the storage area is being designed to be converted to interior space in the future and the sprinkler system is already sized to accommodate it.. may revisit this in the future if they need to cut costs, but my guess is that if that happens the storage area will go away entirely so it'll be a non issue.
a few sidewalls thru the wall, never hurt anyone
YES YOU DO!!
Correct, an auditorium or gymnasium associated with a school can be classified as part of the Group E. But how are you proposing that they treat an S-1 storage use as part of the E?Not all the time
303.1.3 Associated With Group E Occupancies
A room or space used for assembly purposes that is associated with a Group E occupancy is not considered a separate occupancy.
How? Why? What is your justification?
If it is unconditioned storage, use and occupancy classification per Ch. 3 is S-1.
508.1 General
Each portion of a building shall be individually classified in accordance with Section 302.1. Where a building contains more than one occupancy group, the building or portion thereof shall comply with the applicable provisions of Section 508.2, 508.3 or 508.4, or a combination of these sections.
Exceptions:
- Occupancies separated in accordance with Section 510.
- Where required by Table 415.6.2, areas of Group H-1, H-2 and H-3 occupancies shall be located in a detached building or structure.
- Uses within live/work units, complying with Section 419, are not considered separate occupancies.
I do not think he understands that the space in question is for storage and shall be classified as such.
If you are asking me a question, please repeat with full sentences and punctuation.
Not accurate.... must design for the most restrictive use within the building. If the S-1 is large enough to be classified (i.e. >10%), then the fire wall must follow Table 706.4 and go with 3-hr rating. See image from commentary below.If it isn't adjacent to a fire wall, then the one hour ratig is adequate.
Adding a structurally independent self supporting fire wall might cost as much as providing a sprinkler system in that space.right now my feeling is that it will be much easier/cheaper to change the separation wall between E & S-1 to be a 3 hour fire wall and not sprinkle the storage space. it is a solid masonry wall with no openings or penetrations. i may also suggest reducing the size of the storage space so that it's less than 10% of the floor area and can be considered an accessory use.