Yankee,
The "drive thru" portico has walls and ceilings. Do the finishes on the walls and ceiling meet
the requirements of Section R315 - FLAME SPREAD AND SMOKE DENSITY ( from the `06 IRC )?
Section R315.1 - "Wall and ceiling. Wall and ceiling finishes shall have a flame-spread
classification of not greater than 200.
Exception: Flame-spread requirements for finishes shall not apply to trim defined as
picture molds, chair rails, baseboards and handrails; to doors and windows or their
frames; or to materials that are less than 1/28 inch (0.91 mm) in thickness cemented
to the surface of walls or ceilings if these materials have a flame-spread characteristic
no greater than paper of this thickness cemented to a noncombustible backing. "
If the finishes do not meet this minimum requirement, other approved materials / finishes will
need to be installed.
Hope this helps!
FWIW, even "walkways" will need to comply with this section.
* * *
Yankee,
The "drive thru" portico has walls and ceilings. Do the finishes on the walls and ceiling meet
the requirements of Section R315 - FLAME SPREAD AND SMOKE DENSITY ( from the `06 IRC )?
Section R315.1 - "Wall and ceiling. Wall and ceiling finishes shall have a flame-spread
classification of not greater than 200.
Exception: Flame-spread requirements for finishes shall not apply to trim defined as
picture molds, chair rails, baseboards and handrails; to doors and windows or their
frames; or to materials that are less than 1/28 inch (0.91 mm) in thickness cemented
to the surface of walls or ceilings if these materials have a flame-spread characteristic
no greater than paper of this thickness cemented to a noncombustible backing. "
If the finishes do not meet this minimum requirement, other approved materials / finishes will
need to be installed.
Hope this helps!

FWIW, even "walkways" will need to comply with this section.

* * *