1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Generator Distance From Wood Building

Discussion in 'Commercial Building Codes' started by radioatlas, Jun 29, 2020.

  1. radioatlas

    radioatlas Registered User

    Joined:
    Sep 27, 2018
    Messages:
    13
    Likes Received:
    0
    My electrical engineer is asking me if his generator layout meets building code (Washing State, IBC 2015) or NFPA in terms of the distance of the generator to our existing wood building. We are currently 5'-9" from the building exterior edge, however there is a 1'-0 overhang. Are you aware of any code references that dictate this scenario? Thanks in advance!
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    7,242
    Likes Received:
    1,094
    What do the manufacturers installation instructions say?
     
    my250r11 likes this.
  3. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    18,234
    Likes Received:
    1,294



    And the fuel??



    flux capacitor?
    propane?
    Gasoline?
    Diesel ?
    LNG?
    Hydrogen?
    Other?


    And

    Size of tank?

    Double wall?? Or other?
     
  4. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,480
    Likes Received:
    324
    2015 International mechanical Code

    501.3.1 Location of exhaust outlets. For other product-conveying outlets: 10 feet (3048mm) from the property lines; 3 feet (914 mm) from exterior walls and roofs; 10 feet (3048 mm) from operable openings into buildings; 10 feet (3048 mm) above adjoining grade.


    NFPA 37 Standard for the Installation and Use of Stationary Combustion Engines and Gas Turbines
    4.1.4 Engines Located Outdoors. Engines and their weatherproof housing, if provided, that are installed outdoors shall be located at least 5’ from openings in walls and at least 5’ from structures having combustible walls. A minimum separation shall not be required where either of the following conditions exist:

    1. All walls of the structure that are closer than 5’ from the engine have a fire resistance rating of at least 1 hour.

    2. The weatherproof enclose is constructed of noncombustible materials and it has been demonstrated that a fire within the enclosure will not ignite combustible materials outside of the enclosure
     