SCBO1
MID WEST
I see this a lot, no GFCI in a commercial bathroom to the point I do not think it's required and have been told it's only a residential requirement. 210.8 (B) (1) bathrooms.
Does a commercial building bathroom have the option to not install a GFCI outlet?
No, if you install a receptacle in a commercial bathroom it must be GFCI protected.
There is no requirement for a receptacle to be installed in a commercial bathroom though, that would be a design issue.
Chris
raider1,
Thanks for the back-up, I agree that it's not require but if an outlet is installed in a commercial bathroom it has to be GFCI protected!
Pc1
Pcinspector1 asked:
Yes, they DO have the option to not install a GFCI [ rated ] outlet. All of the
lights are installed in non-GFCI rated " outlets ", however, if they want to install
a receptacle, then they are required to be installed on a GFCI rated circuit
[ see Art. 210.8(B)(1), in the `08 NEC ]. There IS an Exception to this
requirement though! Refer to Art. 517.21 - - hospital critical care areas.
raider1 said:
No, if you install a receptacle in a commercial bathroom it must be GFCI protected.There is no requirement for a receptacle to be installed in a commercial bathroom though, that would be a design issue.
Chris
Yeah, what he said
I agree... if it's there, it must be GFCI protected. There's no requirement to have one.