can handrail extensions extend into the maneuvering clearances at doors?
Thank you
RM
Thank you
RM
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
a sketch may be beneficial,JPohling said:a sketch may be beneficial,
what if the unlabeled risers are 6 inches?fatboy said:Not withstanding the original question, um, did I miss something, misinterpret the drawing?24R X 7" = 168" = 14';
1009.10 Vertical rise. A flight of stairs shall not have a vertical
rise greater than 12 feet (3658 mm) between floor levels
or landings.
Please cite a code section!.....Thanks!= + ="Also if it is a continuous stair the center railings do not need extensions as shown, If thatis what I am seeing in the sketch."
CBC 1133B.4.2.2 references Figure 11B-37. Figure 11B-37 text indicates: "inner handrail at landings of stairs that double back or immediately turn shall be continuous and shall not extend into landing or accessible route of travel" image indicates no handrail extensions on inner continuous rails.north star said:= + =Please cite a code section!.....Thanks!
= + =