patrickjames
REGISTERED
2018 IRC P2604.4 Protection of Footings
Trenching installed parallel to footings and walls shall not extend into the bearing plane of a footing or wall. The upper boundary of the bearing plane is a line that extends downward, at an angle of 45 degrees (0.79 rad) from horizontal, from the outside bottom edge of the footing or wall.
So for example an 8 foot deep pool end typically needs to be 8 feet away from the foundation footing if this is a slab on ground with the minimum 12 inch deep footing.
Are there any other code references in regards to this that i am missing?
Trenching installed parallel to footings and walls shall not extend into the bearing plane of a footing or wall. The upper boundary of the bearing plane is a line that extends downward, at an angle of 45 degrees (0.79 rad) from horizontal, from the outside bottom edge of the footing or wall.
So for example an 8 foot deep pool end typically needs to be 8 feet away from the foundation footing if this is a slab on ground with the minimum 12 inch deep footing.
Are there any other code references in regards to this that i am missing?