Above ground metal gas piping is not always required to be bonded. Both the NEC and IFGC state that it needs to be bonded if it is "likely to become energized." And the NEC specifies that if it is a branch circuit that is likely to energize the metal gas piping, then the branch circuit EGC can be used for bonding. The most likely scenario for this is an appliance that uses both gas and electricity, in which case the appliance itself is likely (required by the listing standard?) to do the necessary bonding.
But if you have a gas appliance with no electrical supply, such a natural draft water heater with a standing pilot light, and the gas piping does not cross over any electrical wiring, the gas piping is not likely to become energized, and no bonding is required.
Cheers, Wayne