K Class

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,962
Location
Basement
So a fully self contained fryer/ ventless meeting 96 and IMC

Does it require a K Class fire extinguisher
 
906.4 Cooking Equipment
Fire extinguishers provided for the protection of cooking equipment shall be of an approved type compatible with the automatic fire-extinguishing system agent. Cooking equipment involving solid fuels or vegetable or animal oils and fats shall be protected by a Class K-rated portable extinguisher in accordance with Sections 906.1, Item 2, 906.4.1 and 906.4.2 as applicable.
 
Yep, plan B in the event of failure of the required extinguishing system. Pretty sure there is a requirement in 96 for the supplemental portable K also or it’s in NFPA 17A for the extinguishing agent for commercial cooking equipment. Don’t have access on the codes right now......
 
Ok, no hood but the unit has a built-in wet chemical agent, fill cylinder using only Amerex KP Wet Chemical Agent (6GT015)
 