Forum Coordinator
Chat GPT had some interesting answers once I fed it some very detailed information about a hypothetical deck. You folks should try it.
I have spent over a decade researching and dealing with the subject of deck lateral loads. This is not an off-hand statement or casual guess:I noticed that DCA6 Figure 10 includes the statement "diagonal bracing is prohibited on center posts," while the NC Appendix M Figure AM109.1 clearly shows them. Can anyone comment on the engineering reasons for or against diagonal bracing on center posts?
Cheers, Wayne
Thank you for the extensive response.A center posts with two knee braces takes twice as much force on the post than a corner brace with only one.
Seems that the definition of a Structure is: that it ( whatever it is) can stand-up and remain standing, covers the situation.This deck is far from a wall, pool or building
OK, For a free standing deck Lateral loads shall be transferred to the ground. But where does it say does it say Lateral loads need to be dealt with at all for free standing decks in the first place?
Can someone show me an example of transferring lateral loads to the ground?
Robert, I seem to think that the L/r is the slenderness ratio and it is used to figure out the bearing capacity of the column. I believe the lateral bracing is a separate matterI'm not an engineer, but the code used to place columns into 3 categories....short, medium and long, based on the L/D ratio (length over column dimension). The longer the column, the greater the moment at the base. So the bracing was able to transfer the diaghram stress into the column at a lower height, (thus reducing the effective length of the column) which could mean using a smaller column.
I believe it transfers even more than half the load to the center column.I noticed that DCA6 Figure 10 includes the statement "diagonal bracing is prohibited on center posts," while the NC Appendix M Figure AM109.1 clearly shows them. Can anyone comment on the engineering reasons for or against diagonal bracing on center posts?
Cheers, Wayne
The tributary area of a deck center footing using table R507.3.1 will always be more then the end footings which would require the center piers to be lager then the end piers.I believe it transfers even more than half the load to the center column.
I think the prescriptive approach already ignores the fact that the center column takes half of the tributary load
That footing should probably / technically be 2X the other footings to be proportional. Not sure anyone cares about differential settlement of a deck
Thanks Rich, I'll look it upThe tributary area of a deck center footing using table R507.3.1 will always be more then the end footings which would require the center piers to be lager then the end piers.
I posted this earlier:
It does take more load, and if knee braces are used, it transfers even more from the corners to the center but how much is a guess because it would be based on the deflection of the beam. Which, I imagine, is why AWC doesn't even try.I posted this earlier:
someone posted that the center column of that did neeed a bigger footing
To add to the comp[lexity, let's not forget about UPLIFTThe wind resistant provisions apply so the post would have to be either braced, or moment connection at the top or bottom.
