I cannot find much documentation on the apparent differences between ANSI's 1.5" maximum stair nosing projection and IBC's 1.25" maximum projection- has anyone found any articles or commentary on this issue?
More specifically, 2009 and 2017 versions of ANSI A117.1 Section 504.5 Nosings notes "The permitted projection of the nosing shall be 1 1/2" maximum over the tread or floor below." The 2015 and 2018 versions of the IBC Section 1011.5.5.1 notes "Nosing Projection size. The leading edge (nosings) of treads shall project not more than 1 1/4 inches beyond the tread below."
Obviously the more restrictive 1 1/4" would rule in a building under both codes, but most diagrams found online with a quick google search show the 1 1/2" dimension. Since there is a good deal of referencing and coordination between the two codes, I'm surprised they haven't agreed upon a unified dimension.... or am I missing something?
More specifically, 2009 and 2017 versions of ANSI A117.1 Section 504.5 Nosings notes "The permitted projection of the nosing shall be 1 1/2" maximum over the tread or floor below." The 2015 and 2018 versions of the IBC Section 1011.5.5.1 notes "Nosing Projection size. The leading edge (nosings) of treads shall project not more than 1 1/4 inches beyond the tread below."
Obviously the more restrictive 1 1/4" would rule in a building under both codes, but most diagrams found online with a quick google search show the 1 1/2" dimension. Since there is a good deal of referencing and coordination between the two codes, I'm surprised they haven't agreed upon a unified dimension.... or am I missing something?