Hello, working on the design of an MCC in a predominantly H-3 occupancy. First question concerns occupancy of the MCC. Our arch group typically assigns an S-2 to Electrical Rooms. It is fairly sizeable...so it is not under the 10% threshold for accessory/incidental use. IBC calls for a 2-Hr separation between and S-2 and an H-3.
Second question: H-3 is sprinklered. Client wants no sprinklers in the MCC. by NFPA 13- Section 8.15.10.1 Installation of Sprinkler Systems, requires sprinklers in all spaces in a building protected with sprinklers, including electrical rooms. According to Section 8.15.10.3, however, sprinklers may be eliminated in electrical rooms if the room is dedicated solely to electrical equipment; only dry-type electrical equipment is used; the equipment is installed in a two-hour fire-rated enclosure including protection for penetrations; and no combustible storage is permitted in the room
Client does not see the reason to rate the partitions at all...
it's 475 sf space...transformers sit outside the space.
Thx!
Thx!
