MCC -occupancy type & separation
wedge
Member
Houston
Hello, working on the design of an MCC in a predominantly H-3 occupancy. First question concerns occupancy of the MCC. Our arch group typically assigns an S-2 to Electrical Rooms. It is fairly sizeable...so it is not under the 10% threshold for accessory/incidental use. IBC calls for a 2-Hr separation between and S-2 and an H-3.
Second question: H-3 is sprinklered. Client wants no sprinklers in the MCC. by NFPA 13- Section 8.15.10.1 Installation of Sprinkler Systems, requires sprinklers in all spaces in a building protected with sprinklers, including electrical rooms. According to Section 8.15.10.3, however, sprinklers may be eliminated in electrical rooms if the room is dedicated solely to electrical equipment; only dry-type electrical equipment is used; the equipment is installed in a two-hour fire-rated enclosure including protection for penetrations; and no combustible storage is permitted in the room
Client does not see the reason to rate the partitions at all...
it's 475 sf space...transformers sit outside the space.
Thx!
Welcome
Translate mcc please
Would not call an electrical room a "S"
Maybe part of main occupancy or if over for transformer require separation.
Sorry we sprinkle all, normally to include electrical. They do burn
The sprinkler question is one for the ahj
thank you! MCC is Motor Control Center....8' high cabinets. Sometimes same room will house electrical.
Yea do not think the ahj will negate the sprinklers
You can ask does not hurt
Not an electrical person, but may want the separation so you do not have to do hazardous area electrical
wedge,
1st, ...Welcome to The Building Codes Forum ! 8-)
2nd, ...the 2 hr. rating is necessary to contain a fire
event in the MCC.......You most definitely do not want
sprinklers in the MCC !..........Water & electricity do not
mix very well, especially for the emergency responders,
or others entering the MCC if \ when the sprinklers
activate..........The Fire Code Official [ FCO ] & the
Building Official [ BO ] can override the adopted code
if they feel \ believe that a definite hazard exists that
would negatively effect their human resources \ staff
upon responding to an event where the sprinklers were
activated in the MCC.
The FCO; in a certain jurisdiction where I used to
work, required the 2 hr. rated separation on all electrical
rooms & spaces.
IMO, ...I would not put any sprinklers in a MCC, or other
electrical space.
north star said:
= = : + +wedge,
rooms & spaces.
electrical space.
They might also be hurt when they open the door full of hot smoke and sparking electrical
If the electrical is on fire it is fried already
Most FD's carry infra-red cameras these days, that can detect
a hot door..............If a hot door is detected, the FD will usually
back up and rethink their plan of attack......Another option
would be to have all electrical power killed to a building, or
to a smaller section of a building rather than to enter an
electrical space with activated \ activating sprinklers.
I still vote NO sprinklers in a MCC or electrical space.
Heck, I ain't even part of the Fire Service either ! :o
1) I have never seen electrical rooms (or mechanical rooms for that matter) classified as anything other than the occupancy group they are part of. No need for an S2.
2) Code is clear – IBC requires a fully sprinklered building per NFPA 13. NFPA 13 requires a fully sprinklered building to be sprinklered fully, except where omissions are specifically allowed, such as non-combustible shafts, stairs except for the top and bottom, and electrical rooms enclosed in 2 hr FRR construction.
Owner has the choice of rating or sprinklering the room.
The AHJ has no more discretion to require a properly rated electrical room to be sprinklered than they do to require a non-combustible shaft to be sprinklered, unless a specific amendment to NFPA 13 is adopted by the legislative body.
Thank you very much Dr. J.
We have had numerous discussions over here concerning assigning an occupancy type to these sort of spaces, especially when they exceed the typical 10% sf incidental/accessory definition.
Regardless, however, I will still be showing the rated partition as an answer for the NFPA 13 requirement (in lieu of sprinklers). Removing the 'mixed occupancy' definition along with it's rated separation requirements (2hrs between H-3 and S-2) does a lot to clean up my code review. Thanks again!
Dr. J said:
1) I have never seen electrical rooms (or mechanical rooms for that matter) classified as anything other than the occupancy group they are part of. No need for an S2.2) Code is clear – IBC requires a fully sprinklered building per NFPA 13. NFPA 13 requires a fully sprinklered building to be sprinklered fully, except where omissions are specifically allowed, such as non-combustible shafts, stairs except for the top and bottom, and electrical rooms enclosed in 2 hr FRR construction.
Section 104.8 in the `12 IFC, allows the Fire Code Official to modify the MCC room
design to not have sprinklers in it.
[A] 104.8 Modifications: "Whenever there are practical difficulties involved in
carrying out the provisions of this code, the fire code official shall have the
authority to grant modifications for individual cases, provided the fire code official
shall first find that special individual reason makes the strict letter of this code
impractical and the modification is in compliance with the intent and purpose of
this code and that such modification does not lessen health, life and fire safety
requirements.............The details of action granting modifications shall be
recorded and entered in the files of the department of fire prevention."
The "special individual reason" is that in the opinion of the FCO, ...placing
sprinklers in a MCC room; or other electrical room, would pose a greater
hazard to personnel responding to a MCC room or electrical related fire.
[ i.e. - the water would exacerbate the situation ]......A savvy FCO will
state their position of "having skin in the game" !
If the FCO' decision is challenged, ...the plaintiffs can always chose to go to
court to fight it out, but they will not win !..........I'm pretty sure that case law
will side with the FCO.........It would be a very rare case where the courts
will override FCO in a case like this.
One other thing is the costs !.......If the plaintiffs chose to go to court,
there will be a great amount of additional time & costs associated with their
challenge........Even if the courts were to rule in favor of requiring the
sprinklers in the MCC room, a lot of time & money would have been spent
in the process.
What do you think a business owner will consider as a greater priority ?
[ i.e. - the path of least resistance for their project ].