The way I read it the state law does does not keep the local AHJ from mandating a fire suppression system in a residence through the local adoption process
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I heard some AHJ waive smoke doors inspection if the building is fully sprinkled, any input ?
AHJ should never waive a requirement.I heard some AHJ waive smoke doors inspection if the building is fully sprinkled, any input ?
I have a similar scenario. I am designing remodeling for a three story commercial building. The first and second floors are B-business occupancy and the top floor is R-3 Residential apartment. I am creating "separated" occupancies by designing a two hour horizontal fire barrier between floors. The group B occupancy is not required to be sprinklered, but the group R occupancy is required to be sprinklered per 903.2.8We are in the process of building a 6000 square feet two story building. The first floor, 3000 square feet, will have a classification as Business Group B consisting of office space. The upstairs is classified as Residential R-3. A one hour fire rated ceiling will separate the first and the second story and a one hour fire rated wall will separate the two dwellings upstairs. What areas need to be sprinkled and what NFPA sprinkler system can I use? NFPA 13, 13R, or 13D? I appreciate your input.
I am going to keep it short and sweet...I have a similar scenario. I am designing remodeling for a three story commercial building. The first and second floors are B-business occupancy and the top floor is R-3 Residential apartment. I am creating "separated" occupancies by designing a two hour horizontal fire barrier between floors. The group B occupancy is not required to be sprinklered, but the group R occupancy is required to be sprinklered per 903.2.8
903.2.8 GROUP R.
AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
EXCEPT PER 903.2.8.1 GROUP R-3. AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3.1.3 SHALL BE PERMITTED IN GROUP R-3 OCCUPANCIES.
903.3.1.3 NFPA 13D SPRINKLER SYSTEMS.
AUTOMATIC SPRINKLER SYSTEMS INSTALLED IN ONE- AND TWO-FAMILY DWELLINGS; GROUP R-3, AND TOWNHOUSES SHALL BE PERMITTED TO BE INSTALLED THROUGHOUT IN ACCORDANCE WITH NFPA 13D.
903.3.2 QUICK-RESPONSE AND RESIDENTIAL SPRINKLERS.
WHERE AUTOMATIC SPRINKLER SYSTEMS ARE REQUIRED BY THIS CODE, QUICK-RESPONSE OR RESIDENTIAL AUTOMATIC SPRINKLERS SHALL BE INSTALLED IN ALL OF THE FOLLOWING AREAS IN ACCORDANCE WITH SECTION 903.3.1 AND THEIR LISTINGS:
DWELLING UNITS AND SLEEPING UNITS IN R OCCUPANCIES.
This has triggered all kinds of other questions as you can read below in these posts:
1. What kind of sprinkler system is required? NFPA 13?, NFPA 13R?, NFPA 13D?
2. Are we required to sprinkler the entire building if only one apartment requires a sprinkler system?
420.5 requires R occupancies to be equipped throughout with automatic sprinklers per 903.3.2 - this allows for NFPA13D
3. Are we allowed to use an NFPA 13D sprinkler in a mixed occupancy?
In Pennsylvania, the requirement for sprinklers for single family dwellings has been repealed,
4. Does an apartment qualify as an R-3 single family dwelling exempt from the sprinkler requirement in PA?
5. Is a R-"Fire area" in a non separated mixed occupancy still considered a trigger for a sprinkler system, throughout the "entire building", if the R-fire area is "separated" in accordance with provisions separated mixed occupancies?
I believe there is a conflict in the building code, at least perhaps some confusion:
Table 508.4 shows required separations in mixed occupancies
For each separation there are fire barrier requirements both for sprinklered (S) and non-sprinklered (NS) buildings
For a "non-sprinklered" building, the separation of B-Business and R-Residential is two hours
would it be true then that 903.2.8 is void?
903.2.8 AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
No exceptions are noted
a fire area is defined as
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
By Others: Aggregate Floor Area” shall mean the sum of the gross horizontal areas of all of the floors on a lot measured from the exterior faces of exterior walls or from the center line of party walls.
The code does not define aggregate floor area and there are many interpretations of aggregate
I say a sprinkler is not required, at all, for an R-fire area in a "separated" mixed occupancy because the occupancies are safely and properly separated for a non-sprinklered (NS) building, in accordance with table 508.4, and the Group R fire area is not really a fire area unless it is included in an "unseparated" mixed occupancy.
What say ye all?
I have a similar scenario. I am designing remodeling for a three story commercial building. The first and second floors are B-business occupancy and the top floor is R-3 Residential apartment. I am creating "separated" occupancies by designing a two hour horizontal fire barrier between floors. The group B occupancy is not required to be sprinklered, but the group R occupancy is required to be sprinklered per 903.2.8
903.2.8 GROUP R.
AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
EXCEPT PER 903.2.8.1 GROUP R-3. AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3.1.3 SHALL BE PERMITTED IN GROUP R-3 OCCUPANCIES.
903.3.1.3 NFPA 13D SPRINKLER SYSTEMS.
AUTOMATIC SPRINKLER SYSTEMS INSTALLED IN ONE- AND TWO-FAMILY DWELLINGS; GROUP R-3, AND TOWNHOUSES SHALL BE PERMITTED TO BE INSTALLED THROUGHOUT IN ACCORDANCE WITH NFPA 13D.
903.3.2 QUICK-RESPONSE AND RESIDENTIAL SPRINKLERS.
WHERE AUTOMATIC SPRINKLER SYSTEMS ARE REQUIRED BY THIS CODE, QUICK-RESPONSE OR RESIDENTIAL AUTOMATIC SPRINKLERS SHALL BE INSTALLED IN ALL OF THE FOLLOWING AREAS IN ACCORDANCE WITH SECTION 903.3.1 AND THEIR LISTINGS:
DWELLING UNITS AND SLEEPING UNITS IN R OCCUPANCIES.
This has triggered all kinds of other questions as you can read below in these posts:
1. What kind of sprinkler system is required? NFPA 13?, NFPA 13R?, NFPA 13D?
2. Are we required to sprinkler the entire building if only one apartment requires a sprinkler system?
420.5 requires R occupancies to be equipped throughout with automatic sprinklers per 903.3.2 - this allows for NFPA13D
3. Are we allowed to use an NFPA 13D sprinkler in a mixed occupancy?
In Pennsylvania, the requirement for sprinklers for single family dwellings has been repealed,
4. Does an apartment qualify as an R-3 single family dwelling exempt from the sprinkler requirement in PA?
5. Is a R-"Fire area" in a non separated mixed occupancy still considered a trigger for a sprinkler system, throughout the "entire building", if the R-fire area is "separated" in accordance with provisions separated mixed occupancies?
I believe there is a conflict in the building code, at least perhaps some confusion:
Table 508.4 shows required separations in mixed occupancies
For each separation there are fire barrier requirements both for sprinklered (S) and non-sprinklered (NS) buildings
For a "non-sprinklered" building, the separation of B-Business and R-Residential is two hours
would it be true then that 903.2.8 is void?
903.2.8 AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
No exceptions are noted
a fire area is defined as
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
By Others: Aggregate Floor Area” shall mean the sum of the gross horizontal areas of all of the floors on a lot measured from the exterior faces of exterior walls or from the center line of party walls.
The code does not define aggregate floor area and there are many interpretations of aggregate
I say a sprinkler is not required, at all, for an R-fire area in a "separated" mixed occupancy because the occupancies are safely and properly separated for a non-sprinklered (NS) building, in accordance with table 508.4, and the Group R fire area is not really a fire area unless it is included in an "unseparated" mixed occupancy.
What say ye all?
No, If each unit is a complete dwelling unit. Key element.... do each unit have an actual kitchen as in natural gas for oven? If so, it would be two dwelling units. It can be converted into an SFR but that would be a occupancy classification change. If the existing use are that which per architect licensing laws is work that constitutes the practice of architecture and therefore require an architect then you can not do the project without an architect and shall have new plans prepared by the architect submitted and new permit issued. Old permits shall be invalidated and your original plans re-assessed and denied for not bearing the stamp of a licensed architect or engineer per the respective licensing laws. In addition, you would by law need to be reported to the licensing board for unlicensed practice of architecture if you had so done the plans for a building that requires a licensed architect. Is the existing building a historic building or such a building subject to provisions of Chapter 34 of the IBC?Since my business partner and I are both 50/50 co-owners of the building, that means he owns my dwelling as much as I own his. I know it’s blurring the lines but at that point couldn’t it be considered one dwelling since we are both the owners occupying both sides. It’s merely a door separating the two, as a door separates a bedroom from the rest of a house. If so, could I classify them as owner occupied Lodging Houses? Perhaps I have intentions of operating an Air B&B. If that’s the case, the lodging house according to code, 310.0.5, is subject to International Residential Code and not International Building Code. IRC 2009 and later mandates one and two family dwellings to have sprinkler systems installed, but the State of Missouri passed a law, 67.281, banning local governments from requiring sprinkler systems in one and two family dwellings. Therefore, the entire building is now exempt due to the fact the second story will now be built using residential codes and the bottom story is classified as Group B and is not required.
I would double check if your jurisdiction adopted Chapter 34 when adopting IBC or the IEBC.No, If each unit is a complete dwelling unit. Key element.... do each unit have an actual kitchen as in natural gas for oven? If so, it would be two dwelling units. It can be converted into an SFR but that would be a occupancy classification change. If the existing use are that which per architect licensing laws is work that constitutes the practice of architecture and therefore require an architect then you can not do the project without an architect and shall have new plans prepared by the architect submitted and new permit issued. Old permits shall be invalidated and your original plans re-assessed and denied for not bearing the stamp of a licensed architect or engineer per the respective licensing laws. In addition, you would by law need to be reported to the licensing board for unlicensed practice of architecture if you had so done the plans for a building that requires a licensed architect. Is the existing building a historic building or such a building subject to provisions of Chapter 34 of the IBC?
I have a similar scenario. I am designing remodeling for a three story commercial building. The first and second floors are B-business occupancy and the top floor is R-3 Residential apartment. I am creating "separated" occupancies by designing a two hour horizontal fire barrier between floors. The group B occupancy is not required to be sprinklered, but the group R occupancy is required to be sprinklered per 903.2.8
903.2.8 GROUP R.
AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
EXCEPT PER 903.2.8.1 GROUP R-3. AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3.1.3 SHALL BE PERMITTED IN GROUP R-3 OCCUPANCIES.
903.3.1.3 NFPA 13D SPRINKLER SYSTEMS.
AUTOMATIC SPRINKLER SYSTEMS INSTALLED IN ONE- AND TWO-FAMILY DWELLINGS; GROUP R-3, AND TOWNHOUSES SHALL BE PERMITTED TO BE INSTALLED THROUGHOUT IN ACCORDANCE WITH NFPA 13D.
903.3.2 QUICK-RESPONSE AND RESIDENTIAL SPRINKLERS.
WHERE AUTOMATIC SPRINKLER SYSTEMS ARE REQUIRED BY THIS CODE, QUICK-RESPONSE OR RESIDENTIAL AUTOMATIC SPRINKLERS SHALL BE INSTALLED IN ALL OF THE FOLLOWING AREAS IN ACCORDANCE WITH SECTION 903.3.1 AND THEIR LISTINGS:
DWELLING UNITS AND SLEEPING UNITS IN R OCCUPANCIES.
This has triggered all kinds of other questions as you can read below in these posts:
1. What kind of sprinkler system is required? NFPA 13?, NFPA 13R?, NFPA 13D?
2. Are we required to sprinkler the entire building if only one apartment requires a sprinkler system?
420.5 requires R occupancies to be equipped throughout with automatic sprinklers per 903.3.2 - this allows for NFPA13D
3. Are we allowed to use an NFPA 13D sprinkler in a mixed occupancy?
In Pennsylvania, the requirement for sprinklers for single family dwellings has been repealed,
4. Does an apartment qualify as an R-3 single family dwelling exempt from the sprinkler requirement in PA?
5. Is a R-"Fire area" in a non separated mixed occupancy still considered a trigger for a sprinkler system, throughout the "entire building", if the R-fire area is "separated" in accordance with provisions separated mixed occupancies?
I believe there is a conflict in the building code, at least perhaps some confusion:
Table 508.4 shows required separations in mixed occupancies
For each separation there are fire barrier requirements both for sprinklered (S) and non-sprinklered (NS) buildings
For a "non-sprinklered" building, the separation of B-Business and R-Residential is two hours
would it be true then that 903.2.8 is void?
903.2.8 AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
No exceptions are noted
a fire area is defined as
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
By Others: Aggregate Floor Area” shall mean the sum of the gross horizontal areas of all of the floors on a lot measured from the exterior faces of exterior walls or from the center line of party walls.
The code does not define aggregate floor area and there are many interpretations of aggregate
I say a sprinkler is not required, at all, for an R-fire area in a "separated" mixed occupancy because the occupancies are safely and properly separated for a non-sprinklered (NS) building, in accordance with table 508.4, and the Group R fire area is not really a fire area unless it is included in an "unseparated" mixed occupancy.
What say ye all?
I am in a similar situation. Farmer's market (B) with a R-3 farmstay/AirBnB upstairs in Michigan. What did you end up having to do?I have a similar scenario. I am designing remodeling for a three story commercial building. The first and second floors are B-business occupancy and the top floor is R-3 Residential apartment. I am creating "separated" occupancies by designing a two hour horizontal fire barrier between floors. The group B occupancy is not required to be sprinklered, but the group R occupancy is required to be sprinklered per 903.2.8
903.2.8 GROUP R.
AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
EXCEPT PER 903.2.8.1 GROUP R-3. AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3.1.3 SHALL BE PERMITTED IN GROUP R-3 OCCUPANCIES.
903.3.1.3 NFPA 13D SPRINKLER SYSTEMS.
AUTOMATIC SPRINKLER SYSTEMS INSTALLED IN ONE- AND TWO-FAMILY DWELLINGS; GROUP R-3, AND TOWNHOUSES SHALL BE PERMITTED TO BE INSTALLED THROUGHOUT IN ACCORDANCE WITH NFPA 13D.
903.3.2 QUICK-RESPONSE AND RESIDENTIAL SPRINKLERS.
WHERE AUTOMATIC SPRINKLER SYSTEMS ARE REQUIRED BY THIS CODE, QUICK-RESPONSE OR RESIDENTIAL AUTOMATIC SPRINKLERS SHALL BE INSTALLED IN ALL OF THE FOLLOWING AREAS IN ACCORDANCE WITH SECTION 903.3.1 AND THEIR LISTINGS:
DWELLING UNITS AND SLEEPING UNITS IN R OCCUPANCIES.
This has triggered all kinds of other questions as you can read below in these posts:
1. What kind of sprinkler system is required? NFPA 13?, NFPA 13R?, NFPA 13D?
2. Are we required to sprinkler the entire building if only one apartment requires a sprinkler system?
420.5 requires R occupancies to be equipped throughout with automatic sprinklers per 903.3.2 - this allows for NFPA13D
3. Are we allowed to use an NFPA 13D sprinkler in a mixed occupancy?
In Pennsylvania, the requirement for sprinklers for single family dwellings has been repealed,
4. Does an apartment qualify as an R-3 single family dwelling exempt from the sprinkler requirement in PA?
5. Is a R-"Fire area" in a non separated mixed occupancy still considered a trigger for a sprinkler system, throughout the "entire building", if the R-fire area is "separated" in accordance with provisions separated mixed occupancies?
I believe there is a conflict in the building code, at least perhaps some confusion:
Table 508.4 shows required separations in mixed occupancies
For each separation there are fire barrier requirements both for sprinklered (S) and non-sprinklered (NS) buildings
For a "non-sprinklered" building, the separation of B-Business and R-Residential is two hours
would it be true then that 903.2.8 is void?
903.2.8 AN AUTOMATIC SPRINKLER SYSTEM INSTALLED IN ACCORDANCE WITH SECTION 903.3 SHALL BE PROVIDED THROUGHOUT ALL BUILDINGS WITH A GROUP R FIRE AREA.
No exceptions are noted
a fire area is defined as
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
By Others: Aggregate Floor Area” shall mean the sum of the gross horizontal areas of all of the floors on a lot measured from the exterior faces of exterior walls or from the center line of party walls.
The code does not define aggregate floor area and there are many interpretations of aggregate
I say a sprinkler is not required, at all, for an R-fire area in a "separated" mixed occupancy because the occupancies are safely and properly separated for a non-sprinklered (NS) building, in accordance with table 508.4, and the Group R fire area is not really a fire area unless it is included in an "unseparated" mixed occupancy.
What say ye all?
I am sure when it says a sprinkler system shall be installed throughout the building it means that a sprinkler system shall be installed throughout the building.[F] 903.2.8 Group R.
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.