• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Name That Violation - IBC Version

Protruding object

Also an NFPA 13 violation if that is a supply heat register and not a return air register within 2 ft. of the sprinkler head.
 
Last edited:
The AED head knocker.

I just completed evaluating four area libraries for accessibility and protruding objects was consistent in all four locations. People install AEDs, first aid kits, hand sanitizers, etc. without consideration of the impact they could cause (pun intended).
 
Other items may be:
1) Fire rated door is propped open. Is it required to be close in a fire event?
2) Is the Exit signage compliant? (Is not readable from the pic.)
3) Is the door stop below the Fire Cabinet necessary? It looks like both the AED and Extinguisher cabinets would prevent the door from contacting the floor mounted door stop.
 
It's (section) I think changed a few times lately but....


1003.3.3 Horizontal Projections

Diagram
Objects with leading edges more than 27 inches (685 mm) and not more than 80 inches (2030 mm) above the finished floor shall not project horizontally more than 4 inches (102 mm) into the circulation path.
Exception: Handrails are permitted to protrude 41/2 inches (114 mm) from the wall or guard.
 
Head knocker on the right side.
I don't ever remember seeing a door stop in a hallway or exit corridor, guess I'll have to pay more attention on the next final inspection.
Non-sprinklered building?
Emergency lighting?
 
1003.3.3 Horizontal Projections
Diagram
Objects with leading edges more than 27 inches (685 mm) and not more than 80 inches (2030 mm) above the finished floor shall not project horizontally more than 4 inches (102 mm) into the circulation path
Seems like an odd way to word the requirement. It means that if your obstruction is taller and extends above 80" above the finish floor, it's fine. But in the picture shown, I don't see how the head knocker risk would be reduced if the cabinet were 12" taller.

I would have expected the requirement to be worded more like: between the elevations of 27" and 80" above the finished floor, objects may not project into the circulation path horizontally more than 4."

Cheers, Wayne
 
Seems like an odd way to word the requirement. It means that if your obstruction is taller and extends above 80" above the finish floor, it's fine. But in the picture shown, I don't see how the head knocker risk would be reduced if the cabinet were 12" taller.

I would have expected the requirement to be worded more like: between the elevations of 27" and 80" above the finished floor, objects may not project into the circulation path horizontally more than 4."

Cheers, Wayne
Not many people are 6'8" tall, the same as typical door openings.
 
Not many people are 6'8" tall, the same as typical door openings.
That observation doesn't address my criticism of 1003.3.3. My point is that if the top of the AED were 81" AFF, there would be no 1003.3.3 violation, despite it still being a head knocker.

I'm not familiar with Chapter 10 of the IBC, but looking at 1003.3, seems like 1003.3.1 second paragraph is also relevant:

"A barrier shall be provided where the vertical clearance above a circulation path is less than 80 inches (2032 mm) high above the finished floor. The leading edge of such a barrier shall be located 27 inches (686 mm) maximum above the finished floor."

But that section is also worded poorly, it needs to have an exception for the region within 4" from the wall to coordinate with 1003.3.3.

Cheers, Wayne
 
If the open door is in an accessible path, isn’t the fold-down hold-open interfering with the required 10” clear space?
 
Another possible violation: the door immediately past the protruding AED cabinet swings into the corridor. Trying to visually scale the width of the corridor, I'd say it's about 4', probably not more than 4'6" (54"). If that door is a 36" door, when it's open it will leave only 18" clear. The code says when open 90 degrees the clear width shall not be less than half the required with. Since the required width is probably a minimum 44", 18" is less than 22".

Also, doors swinging into exit access corridors must open 180 degrees and, when fully open, cannot protrude more than 7" from the wall. That protruding cabinet won't allow the door to open that far.

This one photo is a perfect storm of code violations.
 
That observation doesn't address my criticism of 1003.3.3. My point is that if the top of the AED were 81" AFF, there would be no 1003.3.3 violation, despite it still being a head knocker.

I'm not familiar with Chapter 10 of the IBC, but looking at 1003.3, seems like 1003.3.1 second paragraph is also relevant:

"A barrier shall be provided where the vertical clearance above a circulation path is less than 80 inches (2032 mm) high above the finished floor. The leading edge of such a barrier shall be located 27 inches (686 mm) maximum above the finished floor."

But that section is also worded poorly, it needs to have an exception for the region within 4" from the wall to coordinate with 1003.3.3.

Cheers, Wayne
No....because below 80" is more than 27"...I agree that is a little weird, but it works...Anything that is any part above 27 and/or below 80 needs to go below 27".....

Looking forward to your public input on the 2030 IBC.....
 
No....because below 80" is more than 27"...I agree that is a little weird, but it works...
You're going to have to explain what you mean, as you quoted several points of mine, so I'm unclear which point you are responding to.

I maintain that both 1003.3.1 and 1003.3.3 have wording problems.

Cheers, Wane
 
Best I can explain it...maybe...from ANSI which reads the same:
Yes, the diagram is what I expected, but the wording of 10.3.3.3 does not properly cover the case illustrated below, which was my point in my first post in this thread.

Also, the wording of 10.3.3.1 does not have the proper exclusion for the region within 4" of the walls. You can say that the vertical clearance under the obstacle on the wall is 30" (to make up a number, it is not called out in the diagram below), and so 10.3.3.1 says that there should be a barrier that extends down to 27" AFF. Which I assume is not intended to be required if the obstacle complies with 10.3.3.3.

Cheers, Wayne

1723215700919.png
 
Yes, the diagram is what I expected, but the wording of 10.3.3.3 does not properly cover the case illustrated below, which was my point in my first post in this thread.

Also, the wording of 10.3.3.1 does not have the proper exclusion for the region within 4" of the walls. You can say that the vertical clearance under the obstacle on the wall is 30" (to make up a number, it is not called out in the diagram below), and so 10.3.3.1 says that there should be a barrier that extends down to 27" AFF. Which I assume is not intended to be required if the obstacle complies with 10.3.3.3.

Cheers, Wayne

View attachment 14078
To me...what it says...: if it is anywhere, (any part of it) from> 27 to 80, then it needs to be 4" or less or needs to be stretched down to 27"....often we see cane barriers installed or put a piece of furniture under it...Surface mounted electrical panels sometimes bump up against this and they can frame under them to remediate....
 
To me...what it says...: if it is anywhere, (any part of it) from> 27 to 80, then it needs to be 4" or less or needs to be stretched down to 27".
That is what I would expect it to say, but that is not what it says.

10.3.3.3 refers to "Objects with leading edges more than 27 inches (685 mm) and not more than 80 inches (2030 mm) above the finished floor," which means that all parts of the leading edge need to be between 27" and 80" AFF for the sentence to apply (*). Which makes no sense, it should say what you said.

Cheers, Wayne

(*) One can read "more than 27 inches AFF" as meaning any part of the leading edge is more than 27" AFF, but the "not more than 80 inches AFF" clause can only mean that no part of the leading edge is above 80" AFF.
 
Last edited:
And just for sake of discussion, depending on depth, the fire extinguisher cabinet could have done double-duty as cane detection for the AED cabinet IF their difference was less than 4”. As a hypothetical example: