I was hoping that that was the case, but my interpretation of the code is that this is not a repair, but a renovation class 3. In section 907.3 and 907.4 it appears that for the gravity load what you are saying is true, but for the lateral load (907.4) I would need to have a continuous footer.
I was hoping that that was the case, but my interpretation of the code is that this is not a repair, but a renovation class 3. In section 907.3 and 907.4 it appears that for the gravity load what you are saying is true, but for the lateral load (907.4) I would need to have a continuous footer.
The beam needs to be anchored to the pier.
No building official/inspector should make you even expose the footings under those existing piers, let alone pour a new one - IF the current piers are acceptable / able to take a fastener, then all you need to do to be compliant is find a way to fasten the beams to the piers.
This is a REPAIR, you're not building new. Find a way to attach them to what you have. And I still think a flat 2x tapconned/bolted to the top of them will get you where you need to be.
R404.1.5.3 piers and curtain wall foundations
- permitted providing the following provisions are met..
All load bearing walls shall be placed on continuous concrete footings placed integrally with the exterior wall footings.