I have a proposal to use a double fire wall designed in accordance with NFPA 221 (using the 2021 edition of NFPA 221 and the 2018 edition of IBC). This is acceptable per IBC 706.2. I have researched it and find a few items still unclear. The proposal is to build (2) 2-hr, wood framed walls to separate a type III building requiring a 3-hr wall. Per NFPA 221 this is acceptable. Section 6.2.1 requires that fire walls remain stable after collapse, and that a double fire wall constructed in accordance with section 6.5 meets that stability requirement. As far as I can tell then, each wall meets the stability requirement even though the wall is bearing and connected to the structural framing and supporting floors on each side, and will collapse in a fire event. This is because since there is no connection to the other wall, the 2-hr wall will remain to provide protection to that side of the assembly. Opening protectives (doors) are where I am a little unsure.
Section 6.10.3 requires each wall to have a door. Makes perfect sense, except these doors are for egress in both directions, and are acting as a horizontal exit. Now we have a problem. That is pretty much where the code language ends, and we go to the annex. We end up at A.5.8.4. This section provides an example of how to use a "freestanding" vestibule in figure A.5.8.3(b) when used for egress. Unfortunately, the drawing is pretty basic, and there is no additional information. My understanding of "freestanding" here is that it is independently supported to the foundation (in this case the podium).
My hang up is the "freestanding" part. If the fire wall itself is not freestanding, and allowed to collapse why is the vestibule wall? Does this mean that the square footprint of the vestibule gets supported all the way to foundation or am I misunderstanding this. I am not sure why the door couldn't fall away with the rest of the framing and leave the other door and wall in tact for protection.
I am also looking for confirmation that my understanding of this wood framed, bearing wall that will collapse being acceptable is correct. I think I have that part right...
RLGA wrote an excellent paper on this, and his opinion is that the doors must be independently supported and not connected in any way to the collapsible fire walls. This seems to align with my understanding.
ANY guidance is appreciated, and obviously if RLGA can contribute to verify or refute my understanding I would be forever grateful. This is a challenging condition, and the DP's are just as unsure as I am and are waiting on me to guide them.
Section 6.10.3 requires each wall to have a door. Makes perfect sense, except these doors are for egress in both directions, and are acting as a horizontal exit. Now we have a problem. That is pretty much where the code language ends, and we go to the annex. We end up at A.5.8.4. This section provides an example of how to use a "freestanding" vestibule in figure A.5.8.3(b) when used for egress. Unfortunately, the drawing is pretty basic, and there is no additional information. My understanding of "freestanding" here is that it is independently supported to the foundation (in this case the podium).
My hang up is the "freestanding" part. If the fire wall itself is not freestanding, and allowed to collapse why is the vestibule wall? Does this mean that the square footprint of the vestibule gets supported all the way to foundation or am I misunderstanding this. I am not sure why the door couldn't fall away with the rest of the framing and leave the other door and wall in tact for protection.
I am also looking for confirmation that my understanding of this wood framed, bearing wall that will collapse being acceptable is correct. I think I have that part right...
RLGA wrote an excellent paper on this, and his opinion is that the doors must be independently supported and not connected in any way to the collapsible fire walls. This seems to align with my understanding.
ANY guidance is appreciated, and obviously if RLGA can contribute to verify or refute my understanding I would be forever grateful. This is a challenging condition, and the DP's are just as unsure as I am and are waiting on me to guide them.