steveray said:
Combustible Concealed Spaces (UL)TYCO CPVC Pipe and Fittings are not approved for installation in combustible
concealed spaces requiring sprinklers, as referenced in NFPA 13 unless
protected by sprinklers specifically Listed for this application.
Anyone understand this first part?^^^I am going to have concealed combustible protected areas......Are they just saying that the heads have to be properly listed (for concealed comb)? Or are they saying you flatout can't use the CPVC? Or what other listing would the heads have?
Although NFPA
13R and 13D permit the omission of sprinklers from combustible concealed
spaces, Tyco CPVC Pipe and Fittings can be installed in these areas when
protecting residential occupancies according to these standards.
For installations where sprinkler pipe runs through an attic space that requires
sprinklers per NFPA, CPVC piping shall be protected in order to meet the
requirements of its UL and C-UL Listings. Additionally, the authority having
jurisdiction shall be consulted prior to any installation of CPVC in attic spaces
requiring sprinklers. Protection methods and requirements may vary by
jurisdiction and are subject to interpretation.
Once again please check with the manufacture of the pipe for the specific job, but
out of this one:
http://www.harvel.com/sites/www.harvel.com/files/documents/Fire_Sprinkler-Installation_Instructions-English.pdf
Combustible Attic Spaces with
Specific Use Sprinklers
In accordance with the UL Listing, GF Harvel CPVC Fire Sprinkler
Products may be installed within the attic space provided the attic space
is protected with UL Listed Tyco Fire Products Specific Application Attic
Sprinklers.
Specific Application Attic Sprinklers are sprinklers designed to provide
protection of specific light hazard combustible, as well as non-combustible,
attic spaces requiring sprinkler protection.
Installation Requirements
When using the Specific Application Attic Sprinklers, GF Harvel
CPVC Fire Sprinkler Products may be installed to feed the wet system
sprinklers below the ceiling and exposed to feed wet system specific
application attic sprinklers provided the system is installed in accordance
with the Tyco Fire Products’ Technical Data Sheet TFP610 (dated October
2005) for Specific Application Attic Sprinklers.
My take is that if you have cvpc in the attic to protect the rooms below you need tyco attic heads in the attic, if the attic area is combustible construction
http://www.tyco-fire.com/TD_TFP/TFP/TFP610_05_2008.pdf