redeyedfly
REGISTERED
I have a building official that is insisting that FRR load bearing walls must have protected membrane penetrations. (2018 IBC)
The specific issue is a data center box inset into the wall. The BO insists that 704.4.1 requires all exposed wood to be covered by gyp. His argument: "There is no subsection within this part that allows openings or penetrations in this membrane protection." My argument is that there is no requirement to provide opening or membrane penetration protection. 714.4 does not list bearing walls. Nothing sends you to 716.
ICC commentary: “Although a building element is required to have fire resistance by Table 601, this does not mean that the required openings in these building elements have to be protected.” It goes on to state “For example, an interior bearing wall inside a Type IIA building is required to have a fire-resistance rating of not less than 1 hour. However, the openings in that wall need not be protected.”
The ICC opinion we requested said essentially the same as the commentary.
I have never heard of this interpretation. It would follow that all load bearing exterior walls would require membrane penetration by his interpretation of 704.4.1. All window and door openings would need to be wrapped in gyp.
This interpretation seems to misunderstand the different types of FRR assemblies and their purpose.
Any help for a final argument before we appeal to the state is appreciated.
The specific issue is a data center box inset into the wall. The BO insists that 704.4.1 requires all exposed wood to be covered by gyp. His argument: "There is no subsection within this part that allows openings or penetrations in this membrane protection." My argument is that there is no requirement to provide opening or membrane penetration protection. 714.4 does not list bearing walls. Nothing sends you to 716.
ICC commentary: “Although a building element is required to have fire resistance by Table 601, this does not mean that the required openings in these building elements have to be protected.” It goes on to state “For example, an interior bearing wall inside a Type IIA building is required to have a fire-resistance rating of not less than 1 hour. However, the openings in that wall need not be protected.”
The ICC opinion we requested said essentially the same as the commentary.
I have never heard of this interpretation. It would follow that all load bearing exterior walls would require membrane penetration by his interpretation of 704.4.1. All window and door openings would need to be wrapped in gyp.
This interpretation seems to misunderstand the different types of FRR assemblies and their purpose.
Any help for a final argument before we appeal to the state is appreciated.