Can you lay down non-fire rated plywood over the concrete slab of a high-rise so they can install hardwood floors? I only see approval for wood sleepers in 805
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
That's one of the problems with building codes: they cannot provide all of the possible prescriptive methods of accomplishing the same result.
The intent of Section 805 is to limit voids under combustible flooring. If a subfloor was adhered directly to the concrete floor, then I see that as being no different than a subfloor attached to sleepers constructed in accordance with Section 805.1.1.
I agree with the principal of what you are saying, I just wouldn't go so far as to say plywood underlayment can be considered part of the flooring. Under that statement, it would appear that you'd accept plywood sheathing on bar-joists as a floor assembly because "the plywood could be considered part of the flooring".804.1 exempts wood flooring. I don't see any limit on the thickness of wood flooring, so the plywood could be considered part of the flooring. 805 only applies where you have voids, as RLGA and steveray pointed out..
Instead of putting the plywood or finished wood flooring on sleepers, they are planning on attaching the plywood directly to the concrete slab of whatever story they are working on.If the plywood is spanning the structural framing it is structural....Methinks you won't find a finish flooring that will span 5'...And if you do I will still call BS....If you remove it do I fall to my death? If yes, it is structural....My litmus test