Ramp requirements
ELLEN09US
LOS ANGELES
Hello!
I'm working on an outdoor patio deck for a restaurant. I want to know what's the min height that the code requires to have a ramp. If it is less than 6" do I need to have a ramp and handrails/ guardrails? thanks!
RLGA
Sawhorse
Phoenix, AZ
Yes, a ramp is required, and ramps require handrails, but you do not need guards.
redeyedfly
Minneapolis, MN
Hello!
Depends on the slope, not the height. If it's less than 1:20, not a ramp.
it is not a tripping hazard? where can I find it in California Building code? Thanks!
If it is a ramp, I think you're looking for 1003.5.
tbz
Silver Member
NJ/PA Borderlands
1003.5 is for egress. I need accessibility req.
Re-Read 1003.5, "Exist in the Means of egress"
as for accessibility, the MOE is part of an accessible route, but besides 1003.5 then chapter 11,
So
  • 11B-403.3
  • 11B-403.6
  • 11B-405.....
tbz
Silver Member
NJ/PA Borderlands
Are guardrails the dealies just above the floor? Why are they not needed?
E,H: The OP notes the sloped ramp surface to less than 6-inches in height, thus no where near 30-inches in height, thus RLGA's note "Guards not required."
mark handler
Sawhorse
So. CA
RLGA
Sawhorse
Phoenix, AZ
Others are correct--if the slope is 1:20 or less, it is not a ramp and does not need handrails.
RFM132
UD
I think this might be what you are looking for:
IBC 1104.2 Within a Site
At least one accessible route shall connect accessible buildings, accessible facilities, accessible elements and accessible spaces that are on the same site...
ANSI 303.4
Changes in level greater than 1/2" in height shall be ramped...
redeyedfly
Minneapolis, MN
Likely it is egress also. It's hard to imagine how it wouldn't be. If so, you need to meet both requirements. If it is a ramp, you will need to meet 1003.5 handrail requirements which are more stringent than ADA/ANSI 405.8.
What is the slope?
redeyedfly
Minneapolis, MN
i think i have the space to be less than 1:12.
You need to be less than 1:20 to not be a ramp. All egress/accessible ramps need to be less than 1:12.
Consider also that a ramp needs a landing at the top and bottom. A 6" ramp at 1:12 with 60" landings will be 16' long.
A 6" rise in a sloped walking surface at 1:20 will be 10' long, no landings, guardrails, handrails, contrasting colors required.
Msradell
Sawhorse
Louisville Kentucky
More than likely landings will not be required because the sloped surface is going between 2 floor areas, the floor areas would qualify landings the separate landings would not be required.
mark handler
Sawhorse
So. CA
ADASAD 405.8 doesn't require handrails for a 6" high ramp. I think ANSI A117.1 is the same.
ANSI 303.4
IBC, ADASAD and ANSI Do not apply in CA.