Re: RAMP THAT'S NOT A RAMP
Just because something is exempted in ADAAG, it doesn't make it exempt under IBC/ANSI. FredK, Where in IBC or ANSI is an exemption for private status? Back before codes caught up with ADAAG, yes there were exemptions that were valid. These days are not the same.
Mark is correct. IBC / ANSI does not exempt religious groups as the ADA does. However IBC (2006) Section 1103.2.3 wouild allow a raised pulpit to be not accessible.
One of the things, Fred, that needs to be remembered is that in Arizona you have the state accessibility regs as well as the local building codes (as adopted). The state accessibility regs are based on the ADA. Any "private organization" falling under the exemptions in teh ADA are likewise exempt under Arizona law due to the way it is adopted. That does not mean that it is exempt from the building code requirements. These are separate rules adopted by separate entities. If there is no building code or the building code has been modified when adopted (such as to strike Chapter 11 and substitute "do per AZ Access rules") then you may have a case where it applies. Otherwise you have to address each set of rules according to their scoping.
It's just like having the EPA rules for site work as well as the building code provisions for soil work.
Rguarding IBC 1103.2.3 I would not call a raised platform with a pulpit an employee work area. Even if you put up a gate with a sign "employees only". I don't think the couple being married there are employees.
It's hard for me to beleve that the ADA would not require a nursing home owned by a church to be accessable.
A nursing home owned by a church is not a religious institution but a caring institution. It has to meet the ADA. The church is not.
I agree that the raised area in the front is NOT an employee area. It needs access, but if the slope is not more than 1:20, it's a sloped floor and not a ramp. No handrails required. If the drop is less than 30 inches, no guard is required. I'd still advise them to do something to protect the edge against wheels slipping off - whether its from a wheelchair or a movable scaffold to change lamps in the light fixtures. It's a safety item that isn't required by code but a pretty logical idea.
I think we are using different terms here. The main part of the altar needs to be accessible for weddings, choir, special speakers etc. The small (1person) raised pulpit from where the minister would deliver his sermon would not be required to be accessible.
Oh, OK.
No the pulpit isn't required to be accessible since its not required (at least in most churches) to be used to present the sermon. In those religious denominations where the pulpit is elevated and mandated by church policy to be used for sermon presentation, it could be considered an employee area since only the clergy would be allowed to use it anyway.
Sorry for the confusion. . . . :?
If places of worship are exempt from accessibility requirements then how do you enforce 1025.5.1 and 1108.2.3 when the balcony or mezzanine seating exceeds 25% of the total seating?
jus askin.
A wedding is a religous sacrament when conducted in a church not a performance.
Chiors are part of religous services as are special speakers such as traveling clergy.
None of these things are performances.
Coug Dad said:
I did not classify them as "performances". I am not sure what your point is
The raised area of a place of worship does not require accessiblity (as I stated before).
Chapter 11 requires accessiblity to raised areas used for performance.
It does not require accessiblity to raised areas used for worship.
You can read the section yourself.
I just re-read the section.
1103.2.7 exempts raised areas used for purposes of security, life safety or fire safety including, but not limited to, observation galleries, prison towers, fire towers or lifeguard stands.
Which applies to the church worship area? Or is that another section that you are referring to? :?:
The altar would certainly be classified as an employee work area. The pastor is an employee and the altar is where he works. I was referencing Section 1103.1 (2006) which states that all buildings shall be accessible. The exception in 1103.2.3 states tht employee work areas are only required to comply with 907.9.1.2. 1007, and 1104.3.1. If the employee work area is less than 150 square feet and raised over 7 inches then no accessibility is required. Most altar areas are larger than 150 square feet so the employee area (altar) would have to be accessible as required by 1104.3.1.
Sorry, Coug. But I have to disagree.
The alter area is not "used primarily by employees in the execution of their employment." It is, in fact, in many denominations used by the laity to read, speak or serve. Those are not employees. Only in a few denominations is the alter area exclusive to the clergy. And for those denominations, the clergy would take umbrage with the term "employee" as they are "called to serve" and not hirelings.
Since 1103.1 starts by saying all buildings are required to be accessible. Section 1103.2 then follows with exceptions 1103.2.1 through 1103.2.15 and 1103.2.1 includes any other exceptions identified in 1104 through 1110, which section do you believe allows the altar to not have an accessible route? Without an identified exception, 1103.1 would apply.
Gene Boecker said:
I just re-read the section.1103.2.7 exempts raised areas used for purposes of security, life safety or fire safety including, but not limited to, observation galleries, prison towers, fire towers or lifeguard stands.
1104.4 Duh.
I see your line of thought. Webster's defines performance as:
1 a : the execution of an action b : something accomplished : deed, feat
2 : the fulfillment of a claim, promise, or request : implementation
3 a : the action of representing a character in a play b : a public presentation or exhibition
4 a : the ability to perform : efficiency b : the manner in which a mechanism performs
5 : the manner of reacting to stimuli : behavior
6 : the linguistic behavior of an individual : parole; also : the ability to speak a certain language — compare competence 3
Would not worship be a public presentation?
1104.4 Duh.
1104.4 requires access to multiple level areas including mezzanines. 1104.4 says nothing about worship. Double Duh :lol:
Gene Boecker said:
Worship places are NOT exempt from the buidling code - only the ADA.Enforce the code! ;)
You said that several times througout this thread. That was the point of my rhetorical question while ADA may exempt places of worship from accessibility, the building code still requires accessibility as well as accessible means of egress. How do you have accessibility "from" if you don't have accessibility "to".
(Suffering from a long Arch. Review Board meeting this evening.) :cry:
Sorry, Dan.
(Both for your long evening as well as any confusion on my part). It's access from as well as to. You're right.
(I guess it's my life in life safety that springs such means of egress verbiage).
Gene Boecker said:
1104.4 Duh.
1104.4 requires access to multiple level areas including mezzanines. 1104.4 says nothing about worship. Double Duh :lol:[/quote:jhprhjtj]
Next time you read code section 1104.4, try to keep your head out at least until you come to either 1104.5 or 1105...which ever comes first.
See exception 2 for the occupancy A specifics.
See exception 1 for a general exemption if less than 3000 square feet.
I can hear it now..."but you didn't say to read the whole thing."
Coug Dad said:
I see your line of thought. Webster's defines performance as:1 a : the execution of an action b : something accomplished : deed, feat
Good luck with defending any sort of restrictive definition of worship in court against a First Amendment challenge...you might want to speak to your department's council first.
BTW, this issue is directly a result of trying to apply a document that doesn't cover places of worship to places of worship...and of course trying to sidestep the issues around the first amendment which are inevitable when doing so.
Jurisdictions, such as Florida which have adopted ADAAG as their code don't have to worry about this because they haven't changed the scope of accessibility from what is required at the Federal level.