Residential Plumbing, You make the call
OK Plumbing gurus, anything wrong with this setup?
YOU make the call!
The plumber tells you that the trap (which will be 1-1/4" is within 5' of the stack and does not agree with your interpretation. What code section of the IRC or IPC if you use it would apply to show him/her that they are wrong.
Jobsaver,
Might you be referring to Section P3105.2 in the 2006, ...instead of Section
906.2.1 in the IPC?
globe trekker said:
Jobsaver,Might you be referring to Section P3105.2 in the 2006, ...instead of Section
906.2.1 in the IPC?
2006 IPC: 906.2 Venting of fixture drains.
The total fall in a fixture drain due to pipe slope shall not exceed the diameter of the fixture drain, nor shall the vent connection to a fixture drain, except for water closets, be below the weir of the trap.
Since this is a Residential application, the IRC would be the applicable
code me thinks! :D
Also, agree with Builder Bob! The pipe slope appears to be flat on both installs.
Perhaps he is putting an AAV in the lav cabinet.
I have called this before and got that response. I was shocked.. Not sure if he had actually planned it, but to get that answer right off the cuff was impressive.
Tim,
On your response of the AAV, did they actually install the AAV?,
and according to Section P3114.4 in the `06 IRC?
Section P3114.4 - Location.
"Individual and branch air admittance valves shall be located a minimum of 4 inches
(102 mm) above the horizontal branch drain or fixture drain being vented. Stack-type
air admittance valves shall be located a minimum of 6 inches (152 mm) above the
flood level rim of the highest fixture being vented. The air admittance valve shall be
located within the maximum developed length permitted for the vent. The air
admittance valve shall be installed a minimum of 6 inches (152 mm) above insulation
materials where installed in attics."
and
Section P3114.5 - Access and ventilation.
"Access shall be provided to all air admittance valves. The valve shall be located
within a ventilated space that allows air to enter the valve."
Installing the AAV's is one thing. Having actual access to and room to replace them
is another.
Spaces underneath most lavatories is usually quite small! Just sayin'...
Jeff,
Did you, or do you apply the DWV testing requirements of Section P2503.5 - DWV
systems testing, on these drain lines? :o
In my experience 4" is usually not a problem. I suppose if they placed the fixture arm high and the sink tailpiece was really short you may have a problem-- although I suspect you could sneak it between the bowl and the wall. Typically there should be plenty of access and ventilation when installed in the vanity.
No final on the job yet, so we shall see!
I can't give you IPC or IRC code section because we don't use I-code plumbing but, with the lave draning into a wey on the vertical,they have made an S-trap because the vent take off is below the weir of the trap if you like I can give you UPC code section for that one. It would not pass here take it out ane redo.
Just my two cents
Justin
globe trekker said:
Jeff,Did you, or do you apply the DWV testing requirements of Section P2503.5 - DWV
What's the problem? (opens spigot in basement and demonstrates water draining out of waste stack)
Suppose there is no basement, or this is an above grade story?
Do ALL of the plumbing top out drains also get tested?