Gregg Harris said:Start with 403.4 Exhaust ventilation. The bathrooms require exhaust, interment or continuous according to 406.3 based on fixtures.
Second!mtlogcabin said:309.1 is a requirement for human occupancy not human activities.I would defer to the IBC that a rest room is not intended for "human occupancy" and agree heated make up air is not required.
401.2 Ventilation required. Every occupied space shall be ventilated by natural means in accordance with Section 402 or by mechanical means in accordance with Section 403.
402 allow a window to provide the minimum amount of fresh air; it can be total outside air IMO.
403 list exhaust & ventilation for public toilet or restrooms including minimum outdoor air.
Whether you want to use the IBC or IMC the heating requirements are the same; temperature measurement taken at a point 3 ft. above the floor from a wall heater:
309.1 Space-heating systems. Interior spaces intended for human occupancy shall be provided with active or passive space-heating systems capable of maintaining a minimum indoor temperature of 68°F (20°C) at a point 3 feet (914 mm) above floor on the design heating day.
1204.1 Equipment and systems. Interior spaces intended for human occupancy shall be provided with active or passive space-heating systems capable of maintaining a minimum indoor temperature of 68°F (20°C) at a point 3 feet (914 mm) above the floor on the design heating day.
Francis