indyarchyguy
SAWHORSE
Good afternoon. I am working with 2012 IBC. I have a client who has been asked to design a new addition to an existing F-Occupancy. The new building will be an S-Occupancy and consists of one-story, 100-feet to the bottom of the deck. This facility will house rack storage of materials used to make different finished products and are "picked" with several robot retrievers that move both horizontally and vertically, dropping the retrieved item on a conveyor which is delivered to the desired recipient in an adjacent building.
The Owner indicated they built a similar structure in Germany and were required to provide a stairway system to provide access to the roof. The roof is not occupied and will not have any rooftop equipment located on it. Based on the response to my questions, the only reason to access the roof will be for roof maintenance as needed.
Per my review of 1009, it appears to me the only requirement for a stairway is for a building with four or more stories above grade plane. Since this is a single-story, I do not believe this section applies to this particular facility. Thoughts?
The Owner indicated they built a similar structure in Germany and were required to provide a stairway system to provide access to the roof. The roof is not occupied and will not have any rooftop equipment located on it. Based on the response to my questions, the only reason to access the roof will be for roof maintenance as needed.