In Ontario, for a house with secondary suite, with respect to the ceiling fire protection of the furnace room where sprinkler system is installed, I found there is a lot of confusion about whether or not the ceiling of the furnace room is required to be drywalled:
Here is a fire code brochure from the City of Barrie: https://www.barrie.ca/sites/default/files/2022-07/FireCode-Brochure.pdf
"While sprinkler systems are not mandatory, their installation may lower the requirements for fire containment in a room with a fuel fired appliance. The installation only exempts the ceiling above the appliance(s) from fire rating..."
Question: is it clear that the ceiling of the furnace room is required to be drywalled?
Here is a guide from the City of Collingwood: https://www.collingwood.ca/sites/de...nts/b408pgresaccessoryapartment20210915_2.pdf
On page 18, there is a sketch showing the ceiling of the furnace room is not drywalled. and on page 25:
" Notes to Table B: 1. Horizontal fire separations are waived in a service room where the service room is sprinklered (discussion on placement & number of heads required will be determined on site) and the installation satisfies the following: ..."
According to the sketch and notes of the guide from Collingwood, the ceiling of the furnace room where there is sprinkler system is not required to be drywalled.
The following is from Ontario Building Code Division B – Part 11 Table 11.5.1.1.C.
"C149 9.10.9.10.(1)
Ceiling fire separation need not have a fire-resistance rating where sprinklering,
subject to C.A. C27, of fire compartments on both sides of vertical fire separation is
provided and where such fire separation is not required to exceed 1 h."
Question: Is the ceiling of the furnace room required to be drywalled when the Ceiling fire separation need not have a fire-resistance rating?
"C149 9.10.9.10.(1)