In a public single occupancy restroom, California Building Code 11B-604.3.1 requires two kinds of clearances:
1) A WATER CLOSET clearance 60" wide x 56" deep. the 56" is measured from the rear wall. 11B-604.3.2 says no fixtures may be located within the required WATER CLOSET clearance".
2) A MANEUVERING clearance 60" wide x 48" deep. The 48" is measured from the front of the toilet. The code is silent about allowing other fixtures in this space. In this scenario, if the toilet is 30" long, the walls of single-occupancy restroom must be at least (30" + 48" =) 78" deep.
**QUESTION: for item #2, can the MANEUVERING clearance include the space underneath a sink, as described in 11B-306.2?
Here's my specific situation:
I am trying to modify existing single occupancy male and female toilet rooms for code compliance, and each room is 62" wide x 90" long. After I meet the 56" deep clear toilet space, that leaves me another (90-56=) 34" of extra depth in which I can place a wall-mounted sink, even though this sink encroaches into the manuevering space (#2). I have the required knee and toe clearance under the sink.
Will this work?
1) A WATER CLOSET clearance 60" wide x 56" deep. the 56" is measured from the rear wall. 11B-604.3.2 says no fixtures may be located within the required WATER CLOSET clearance".
2) A MANEUVERING clearance 60" wide x 48" deep. The 48" is measured from the front of the toilet. The code is silent about allowing other fixtures in this space. In this scenario, if the toilet is 30" long, the walls of single-occupancy restroom must be at least (30" + 48" =) 78" deep.
**QUESTION: for item #2, can the MANEUVERING clearance include the space underneath a sink, as described in 11B-306.2?
Here's my specific situation:
I am trying to modify existing single occupancy male and female toilet rooms for code compliance, and each room is 62" wide x 90" long. After I meet the 56" deep clear toilet space, that leaves me another (90-56=) 34" of extra depth in which I can place a wall-mounted sink, even though this sink encroaches into the manuevering space (#2). I have the required knee and toe clearance under the sink.
Will this work?