Will the 1" line be big enough going to the house to supply it or will it need a bigger line or booster pump at house ?" Thanks
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
The engineer at the water company said he couldn't recommend due to policy. He said the pressure at the 6" main was 50 psi to 65 psi was all he would say. The house will be 70' below the 6" water main and it will be 3,500 ft in length. The house he's going build will have 3 bathrooms, laundry room and kitchen. Will be 3 kids and two adultsA 1" line is usually big enough for a house. This is a very broad statement because house sizes, fixture counts, and water pressures vary.
Around here, the only time you get bigger than 1" is when you get into big houses in rich neighborhoods.
50 to 65 psi at the 6" mainI do not have the answer, but I would also be concerned about the pressure drop in a 1" line over half a mile..........................what is the pressure in the 6" line?
If, after a while, it is determined that there is not enough
pressure for simultaneous use of the water demands, then
you can always add a water storage tank and booster
pump later.
Initially, I would not spend the money if it was not
necessary !
Are you thinking that he might need to hydrant to supply additional flow to the sprinklers or just for fire protection use?Might need a hydrant.
The fire dept might require a hydrant for fire protection.Are you thinking that he might need to hydrant to supply additional flow to the sprinklers or just for fire protection use?
I've never seen a situation where the FD Req a hydrant on private property for residential structure. Not saying it doesn't happen but I've never seen it.The fire dept might require a hydrant for fire protection.