Sizing bonding jumper for 250.92(B)(4)

BN4537

SAWHORSE
Joined
Sep 10, 2020
Messages
974
Location
Kansas
Is it necessary to size a bonding jumper to 250.122 if the only purpose of the bonding jumper is to connect to the bonding bushing on a metal raceway for a service? No concentric knockouts or impaired connection, the only purpose is to comply with the section that states "Standard locknuts or bushings shall not be the only means for bonding required by this section".

The only reason I am wondering is that the metal raceway "is" bonded by standard locknuts etc. and the bonding jumper is added on services to make a lower impedance connection so that you can pull enough amps to blow the fuses on the primary side of the utility transformer, which can take 2-4 times the amount of current that your main breaker would require.

This photo is an example from my old photos to demonstrate basically what I am talking about, but not a current install and may not fit my question entirely.


Bonding bushing.jpg
 
Could you instead use a product like this on large parallel conductor installations, threaded onto an EMT male adapter? Is there an amperage limit on these I can't find? Just doesn't seem equivalent to a large bonding jumper on, say, a 1200 amp service.

Seems to be listed for RMC and IMC conduit, is an EMT male adapter considered the same thing for listing purposes of this type of locknut?


Screenshot 2025-09-23 082808.png
 