1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Slab-on-grade Insulation

Discussion in 'Residential Energy Codes' started by fj80, Feb 13, 2017.

  1. fj80

    fj80 Sawhorse

    Joined:
    Jan 18, 2016
    Messages:
    230
    Likes Received:
    32
    Designing a single-family house using IRC 2012/ 2012 Virginia Residential Code. Climate Zone 4 (not Marine).

    I have a conditioned space with a slab-on-grade that is less than 12" below grade, so I know it needs to be insulated per N1102.2.9. But I could have sworn that in addition to providing insulation on either the inside or outside of the foundation wall, that you also had to provide under-slab insulation horizontally for a minimum of 36" from the perimeter of the slab. Is this requirement somewhere else in the code? Or is that an old requirement that has changed?
     
  2. Francis Vineyard

    Francis Vineyard Registered User

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
    In accordance with Section N1102.2.8 and TABLE N1102.1.1 (R402.1.1) Column 10; SLAB R-VALUE & DEPTH

    Insulation located below grade shall be extended the distance of 24 inches by any combination of vertical and horizontal insulation extending under the slab or insulation extending out from the building.
     
    fj80 likes this.
  3. rogerpa

    rogerpa Silver Member

    Joined:
    Nov 5, 2009
    Messages:
    246
    Likes Received:
    48
    N1102.2.9 (R402.2.9) Slab-on-grade floors. Slab-on-grade
    floors with a floor surface less than 12 inches (305
    mm) below grade shall be insulated in accordance with
    Table N1102.1.1. (R-10). The insulation shall extend downward
    from the top of the slab on the outside or inside of the
    foundation wall. Insulation located below grade shall be
    extended the distance provided in Table N1102.1.1 (2') by any
    combination of vertical insulation, insulation extending
    under the slab or insulation extending out from the building.
    Insulation extending away from the building shall be
    protected by pavement or by a minimum of 10 inches (254
    mm) of soil. The top edge of the insulation installed
    between the exterior wall and the edge of the interior slab
    shall be permitted to be cut at a 45-degree (0.79 rad) angle
    away from the exterior wall. Slab-edge insulation is not
    required in jurisdictions designated by the building official
    as having a very heavy termite infestation. Stated values
    based on Zone 4/5
    . If a heated slab add R-5 2' becomes 4'
    if located in Zones 6-8. See footnote d of Table N1102.1.1
    for heated slabs in Zones 1-3.

     
    fj80 and my250r11 like this.
  4. fj80

    fj80 Sawhorse

    Joined:
    Jan 18, 2016
    Messages:
    230
    Likes Received:
    32
    Since the code says "The insulation shall extend downward from the top of the slab..." does this mean you have to place the insulation between the interior face of the foundation wall and the basement slab? If so, then the slab never contacts the foundation wall. Does the slab not need to be tied into the foundation wall with rebar? Or is it fine for the slab to be structurally independent from the foundation wall?
     
  5. Francis Vineyard

    Francis Vineyard Registered User

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
    It depends how it's done. Pre-engineered wall already have the insulation. The below example apparently is no longer linked online:

    Slab1.JPG
    Slab.JPG
     
    fj80 likes this.
  6. tmurray

    tmurray Registered User

    Joined:
    Jun 10, 2011
    Messages:
    1,755
    Likes Received:
    475
    We generally see a break between the slab and the wall for insulation. These walls are generally laterally supported on both sides, so I'm not sure what rebar would do...
     
  7. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,547
    Likes Received:
    847
    During Dynamic action, Earthquakes and tornados, the slab is used as a horizontal diaphragm, to restrain and transfer loads from the walls.
     
    tmurray likes this.
  8. Mark K

    Mark K Platinum Member

    Joined:
    May 12, 2010
    Messages:
    1,561
    Likes Received:
    148
    On many smaller buildings the slab on grade is not formally considered as part of the lateral system. This is a call that should be made by the engineer.

    When the slab on grade is needed to tie the building together any break between the wall and the slab is a problem.
     
  9. tmurray

    tmurray Registered User

    Joined:
    Jun 10, 2011
    Messages:
    1,755
    Likes Received:
    475
    AHA, we don't get those here, at least not that many. Thanks!
     