Hi, this is my first post but I frequently search this site and have found a lot of helpful info. I've done some searching but haven't come across anything. I'm hoping someone can point me in the right direction. Sorry if this is a stupid question...
We're working on an old multi-family building (R-2, I-B construction) in Virginia. It has an existing community room that would be Assembly Group A, however it meets the criteria of IBC 303.1.2 Small Assembly Spaces. It's less than 750 sf and the occupancy is less than 50. We want to add some glazing along the existing corridor wall and I'm struggling to determine what level of fire resistance (or fire protection rating) is required, if any.
303.1.2 Small assembly spaces
The following rooms and spaces shall not be classified as Assembly occupancies:
Thanks in advance,
Ken
We're working on an old multi-family building (R-2, I-B construction) in Virginia. It has an existing community room that would be Assembly Group A, however it meets the criteria of IBC 303.1.2 Small Assembly Spaces. It's less than 750 sf and the occupancy is less than 50. We want to add some glazing along the existing corridor wall and I'm struggling to determine what level of fire resistance (or fire protection rating) is required, if any.
303.1.2 Small assembly spaces
The following rooms and spaces shall not be classified as Assembly occupancies:
- A room or space used for assembly purposes with an occupant load of less than 50 persons and accessory to another occupancy shall be classified as a Group B occupancy or as part of that occupancy.
- A room or space used for assembly purposes that is less than 750 square feet (70 m2) in area and accessory to another occupancy shall be classified as a Group B occupancy or as part of that occupancy.
Thanks in advance,
Ken