Okay so let's drag this out some more. If I build an attached garage to my house and have no communication to the house, then do I need a smoke detector there?
Where?......Dennis said:I am an electrical contractor
Hard wired and interconnected in the new addition. This basement area to the bedroom area above.cda said:Are they asking forBattery operated
Or
Hard wired
Or
Hard wired interconnected ???
If I tell you will you come visit me again.chris kennedy said:Where?......
Did that, it basically comes down to -- It's a basement and code requires one in a basement.cda said:This might be how it reads;;;3. On each additional story of the dwelling, Is this room that does not communicate with the living area a dwelling. I think not just as an attached garage is not a dwelling.
You can ask the indpector for the section he is cursing for the requirement .Than look at it to see how it reads and than discuss it with him if you feel he is reading it wrong
Well I'll be, Ladies and Gentlemen, we are in the presents of Greatness! Welcome aboard, its about time.Dennis said:If I tell you will you come visit me again.
I was planning to mess with you a bit but I decided to fess up-- good to see ya- now teach me something.chris kennedy said:Well I'll be, Ladies and Gentlemen, we are in the presents of Greatness! Welcome aboard, its about time.
no .. .dennis said:okay so let's drag this out some more. If i build an attached garage to my house and have no communication to the house, then do i need a smoke detector there?
Not only would I charge for the X-tra to install the smoke, I would charge for your research time here.Dennis said:now teach me something.
Is the garage any different then this isolated storage room? Suppose there was a garage door on this room and I could drive in as my garage is setup.mark handler said:no .. .
It better be for the price you charged me.chris kennedy said:BTW, this place is the best.
The structure is a 2 story addition that is attached to the side of an existing 3 story house-- this room does not communicate with the house-- no windows, stairs just an exterior door. If that door became a garage door we would not need a SD yet because it has a regular door we need a SD????? Sounds painfully odd. No different then the scenario I stated above with a garage attached to the side of the house.cda said:Without seeing it in person hard to call but may fall underOn each additional story of the dwelling, including basements and habitable attics
Same reason you should not place one in a kitchen or bathDennis said:Is the garage any different then this isolated storage room? Suppose there was a garage door on this room and I could drive in as my garage is setup.
I think you are missing my point. The need for a smoke alarm in this space is synonymous to installing one in a garage that does not communicate to the house. Yes, of course a garage may be a bad idea because of the exhaust but I am trying to show how these spacing are not different other than a car being in one.mark handler said:Same reason you should not place one in a kitchen or bath
R314.1 Smoke detection and notification. All smoke alarmsshall be listed in accordance with UL 217 and installed inaccordance with the provisions of this code and the household
fire warning equipment provisions of NFPA 72.
R314.2 Smoke detection systems. Household fire alarm systems
installed in accordance with NFPA 72 that include smoke
alarms, or a combination of smoke detector and audible notification
device installed as required by this section for smoke
alarms, shall be permitted. The household fire alarm system
shall provide the same level of smoke detection and alarm as
required by this section for smoke alarms. Where a household
fire warning system is installed using a combination of smoke
detector and audible notification device(s), it shall become a
permanent fixture of the occupancy and owned by the homeowner.
The system shall be monitored by an approved supervising
station and be maintained in accordance withNFPA72.
Exception: Where smoke alarms are provided meeting the
requirements of Section R314.4.
R314.3 Location. Smoke alarms shall be installed in the following
locations:
1. In each sleeping room.
2. Outside each separate sleeping area in the immediate
vicinity of the bedrooms.
3. On each additional story of the dwelling, including basements
and habitable attics but not including crawl spaces
and uninhabitable attics. In dwellings or dwelling units
with split levels and without an intervening door
between the adjacent levels, a smoke alarm installed on
the upper level shall suffice for the adjacent lower level
provided that the lower level is less than one full story
below the upper level.
When more than one smoke alarmrequired to be installedwithin an individual dwelling unit the alarm devices shall be
interconnected in such a manner that the actuation of one alarm
will activate all of the alarms in the individual unit.
R314.3.1 Alterations, repairs and additions. When alterations,
repairs or additions requiring a permit occur, or
when one or more sleeping rooms are added or created in
existing dwellings, the individual dwelling unit shall be
equipped with smoke alarms located as required for new
dwellings.
Exceptions:
1. Work involving the exterior surfaces of dwellings,
such as the replacement of roofing or siding, or the
addition or replacement of windows or doors, orthe addition of a porch or deck, are exempt fromthe requirements of this section.
2. Installation, alteration or repairs of plumbing or
mechanical systems are exempt from the requirements
of this section.
R314.4 Power source. Smoke alarms shall receive their primary
power from the building wiring when such wiring is
served from a commercial source, and when primary power is
interrupted, shall receive power from a battery.Wiring shall be
permanent and without a disconnecting switch other than those
required for overcurrent protection. Smoke alarms shall be
interconnected.
Exceptions:
1. Smoke alarms shall be permitted to be battery operated
when installed in buildings without commercial
power.
2. Interconnection and hard-wiring of smoke alarms in
existing areas shall not be required where the alterations
or repairs do not result in the removal of interior
wall or ceiling finishes exposing the structure,
unless there is an attic, crawl space or basement available
which could provide access for hard wiring and
interconnection without the removal of interior finishes.
Since the area is not adjacent to bedrooms we do not need to install a co detector. I was just bring up the NC rule. It is interesting that every building inspector seems to agree this is a basement even though it is unheated and there is no communication, however if I asked if it were a shed built attached to the house with separate entrance no one thinks it would need smoke detectors. I still don't see the difference and on second thought they tend to agree.jar546 said:CO was also added to the 2009 IRC. I did not post because the question was specific to smoke alarms.
Any comment?joyee said:Yes this is great conversation. Although smoking is not the good habit we should to avoid from this. But you idea is really comfortable..
I thought I recognized you. You're Joyee from Spamalot aren't you?joyee said:Any comment?custom koozies