251,000 S.F. mixed use, new construction containing occupancy types "A" and "E"
Type 1B construction (protected, unlimited area building)
Fully Sprinklered
2018 IBC and 2018 NFPA 101 LSC are applicable.
Per 2018 NFPA 101 - 14.3.7.2 (2) "buildings protected throughout by an approved, supervised automatic sprinkler system in accordance w/ Section 9.7" [do not require subdivision of building spaces into compartments]
Couldn't find anything in chapter 12 requiring subdivision / compartmentalization
Couldn't find anything in IBC 2018 requiring subdivision / compartmentalization for this type of building
When I designed a similar building in 2000, NFPA 101 Section 14.3.7.2 required compartmentalization but the sprinkler removed the 30,000 SF limitation on compartment size as long as no less than 2 compartments were provided.
Has the compartmentalization requirement been removed by exception 14.3.7.2 (2)? What am I missing?
Thanks
Type 1B construction (protected, unlimited area building)
Fully Sprinklered
2018 IBC and 2018 NFPA 101 LSC are applicable.
Per 2018 NFPA 101 - 14.3.7.2 (2) "buildings protected throughout by an approved, supervised automatic sprinkler system in accordance w/ Section 9.7" [do not require subdivision of building spaces into compartments]
Couldn't find anything in chapter 12 requiring subdivision / compartmentalization
Couldn't find anything in IBC 2018 requiring subdivision / compartmentalization for this type of building
When I designed a similar building in 2000, NFPA 101 Section 14.3.7.2 required compartmentalization but the sprinkler removed the 30,000 SF limitation on compartment size as long as no less than 2 compartments were provided.
Has the compartmentalization requirement been removed by exception 14.3.7.2 (2)? What am I missing?
Thanks