t-bar ceiling
Oh Well
This fixture is supported by the t-bar. It is Listed and Labeled. The installation instructions show it as you see it. My question is: Should there be another wire from the rafter to the fixture to keep it from falling with the ceiling in the event of an earthquake.
Yes. The requirement is in ASTM E580. Quote from 09 version below. If there is more recent version it has the same/similar
For Seismic Design Category C: "4.4.3 Lighting fixtures weighing less than 10 lb [5 kg] shall have one, No. 12-gauge [2.70 mm] safety wire connected from the fixture housing (not the detachable end plates) to the structure above. It is not necessary for these safety wires to be taut . . ."
For Sesimic Design Category D, E and F: "5.3.4 Lighting fixtures weighing less than 10 lb [5 kg] shall have one, No. 12 gauge [2.70 mm] safety wire connected from the fixture housing to the structure above. It is not necessary for these safety wires to be taut."
  • Like
Reactions: ICE
