• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

t-bar ceiling

ICE

Oh Well
Joined
Jun 23, 2011
Messages
12,922
Location
California
This fixture is supported by the t-bar. It is Listed and Labeled. The installation instructions show it as you see it. My question is: Should there be another wire from the rafter to the fixture to keep it from falling with the ceiling in the event of an earthquake.

 
Yes. The requirement is in ASTM E580. Quote from 09 version below. If there is more recent version it has the same/similar

For Seismic Design Category C: "4.4.3 Lighting fixtures weighing less than 10 lb [5 kg] shall have one, No. 12-gauge [2.70 mm] safety wire connected from the fixture housing (not the detachable end plates) to the structure above. It is not necessary for these safety wires to be taut . . ."

For Sesimic Design Category D, E and F: "5.3.4 Lighting fixtures weighing less than 10 lb [5 kg] shall have one, No. 12 gauge [2.70 mm] safety wire connected from the fixture housing to the structure above. It is not necessary for these safety wires to be taut."
 