Type IIIA construction: R2 occupancy, Steel column structure, concrete slabs over metal deck floors. storefront glass system for the exterior.
According to Table 601, under IIIA we are allowed to have a primary structure of 1 hour. Per 704.10, if the structural members are located within the exterior wall they are required to to have the fire rating for exterior bearing walls based on IIIA (2hrs).
So now I have a steel structure within a 2hr exterior wall assembly , but footnote d says that with an approved automatic sprinkler system can be substituted for 1hr fire resistance rated construction as long as the system is not otherwise required by other provisions of the code. We do not need to use the sprinkler system to expand floor area or height. But does that fact that section 903 require sprinklers in R occupancy count as "being required by other provisions of the code"?
The thinking was that if the steel structure is within the 2hr exterior assembly, and we have sprinklers that we could use the sprinklers to bring the 2hr assembly down to 1hr. Any insight?
According to Table 601, under IIIA we are allowed to have a primary structure of 1 hour. Per 704.10, if the structural members are located within the exterior wall they are required to to have the fire rating for exterior bearing walls based on IIIA (2hrs).
So now I have a steel structure within a 2hr exterior wall assembly , but footnote d says that with an approved automatic sprinkler system can be substituted for 1hr fire resistance rated construction as long as the system is not otherwise required by other provisions of the code. We do not need to use the sprinkler system to expand floor area or height. But does that fact that section 903 require sprinklers in R occupancy count as "being required by other provisions of the code"?
The thinking was that if the steel structure is within the 2hr exterior assembly, and we have sprinklers that we could use the sprinklers to bring the 2hr assembly down to 1hr. Any insight?