Sifu
- Joined
- Sep 3, 2011
- Messages
- 2,813
Clarification please. The code goes into great detail on how a tempered panel is to be labeled. Then it appears to throw it all under the bus with the final statement. I have always required etching but here where they apparently haven't been held to that I have now run across two window suppliers (may actually be the same) who when having to replace some windows a peel off label magically appears. The first time I did not permit it but the owner/builder showed me by simply not scheduling a final inspection on the addition. Now a new SF has 4 windows that must be tempered. I noted it at the framing inspection and again at final. Today at reinspection the magic label appeared. I decided to check my premise and I see the final statement, highlighted below. Also, the commentary appears to say the same thing.
The label does not provide any of the information below, it simply says TEMPERED GLASS. When you peel the paper off it looks like etching but scratches off with my fingernail, which I guess would agree with the commentary.
I am sure one of you has run up against this before. What say you?
R308.1 Identification. Except as indicated in Section R308.1.1
each pane of glazing installed in hazardous locations as defined
in Section R308.4 shall be provided with a manufacturer's designation
specifying who applied the designation, designating the
type of glass and the safety glazing standard with which it complies,
which is visible in the final installation. The designation
shall be acid etched, sandblasted, ceramic-fired, laser etched,
embossed, or be of a type which once applied cannot be removed
without being destroyed. A label shall be permitted in lieu of the
manufacturer's designation.
(commentary)
A manufacturer can identify safety glazing with a
removable paper designation, provided it is destroyed
during removal. This ensures that the designation will
not be applied to a noncomplying piece of glass.
(commentary)