That could certainly be a possibility. Personally not sure what whatever what you breakers that small, you never know what you're going to need in the future. That's why when we built everything his 12 gauge with 20 amp breakers. It costs a little more not that that much to the cost of everything else.Maybe it has something to do with copper-coated aluminum wiring?
If the past several decades trend continues, less. Hopefully, less, nor more. That I could put every light in every room of an average house on a 10 amp circuit makes me like to this. That's a lot of wire. Are you planning to switch back to incandescent?you never know what you're going to need in the future
I do.Does the ROMEX KING know about this?
Hear ye, hear ye! Citizens of the esteemed realm of TBCF, bow and tremble, for His Royal Highness, the ROMEX King, hath graced our humble forum with his electrifying wisdom!I do.
(WOW, last time I said that it cost me dearly.)
At least all the ceiling fixtures and exterior sconces.That I could put every light in every room of an average house on a 10 amp circuit makes me like to this.
240.4(D)They did not add 14AWG copper clad AL to the 2023 NEC. Not that that is a bad thing.
I was wrong, thanks for setting me straight.240.4(D)
(D) Small Conductors.
Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by 240.4(D)(1) through (D)(8) after any correction factors for ambient temperature and number of conductors have been applied.
(1) 18 AWG Copper.
7 amperes, provided all the following conditions are met:
- (1) Continuous loads do not exceed 5.6 amperes.
- (2) Overcurrent protection is provided by one of the following:
- a. Branch-circuit-rated circuit breakers listed and marked for use with 18 AWG copper conductor
- b. Branch-circuit-rated fuses listed and marked for use with 18 AWG copper conductor
- c. Class CC, Class CF, Class J, or Class T fuses
(2) 16 AWG Copper.
10 amperes, provided all the following conditions are met:
- (1) Continuous loads do not exceed 8 amperes.
- (2) Overcurrent protection is provided by one of the following:
- a. Branch-circuit-rated circuit breakers listed and marked for use with 16 AWG copper conductor
- b. Branch-circuit-rated fuses listed and marked for use with 16 AWG copper conductor
- c. Class CC, Class CF, Class J, or Class T fuses
(3) 14 AWG Copper-Clad Aluminum.
10 amperes, provided all the following conditions are met:
- (1) Continuous loads do not exceed 8 amperes
- (2) Overcurrent protection is provided by one of the following:
- a. Branch-circuit-rated circuit breakers are listed and marked for use with 14 AWG copper-clad aluminum conductor.
- b. Branch-circuit-rated fuses are listed and marked for use with 14 AWG copper-clad aluminum conductor.
(4) 14 AWG Copper.
15 amperes
That is why I started this forum. So I could learn more and we can all share information and crazy opinions.I was wrong, thanks for setting me straight.