What I have here is a 2000 amp switch board and from the load side of service disconnecting means is a #10 thhn tap approx 8' in length in emt to a 30 amp fused switch then close nippled to the TVSS / SPD. My question is do TVSS / SPD's have to follow tap rules? Here are my references. 08' NEC 285.24(A), 230.82(8), 240.21(B)(1)......I say it is a violation. The EE is saying this was approved and stamped drawings and we do it all the time in DC, Md, and Va.