Francis Vineyard
REGISTERED
Do you now require the 30 inch clearance in front of the fire suppression cabinet?
Manufacturer only has 18 inches to combustibles.
New for 2009 IMC;
306.1 Access for maintenance and replacement. Appliances
shall be accessible for inspection, service, repair and replacement
without disabling the function of a fire-resistance-rated
assembly or removing permanent construction, other appliances,
venting systems or any other piping or ducts not connected
to the appliance being inspected, serviced, repaired or
replaced. A level working space at least 30 inches deep and 30
inches wide (762 mm by 762 mm) shall be provided in front of
the control side to service an appliance.