for the dishwasher? or enclosed oven? orrgrace said:For the most part, if it looks like a Type I hood, it should be designed as a Type I hood. IMC 506.3 Ducts serving a Type I hood. Every section in 506.3, including sub-sections, is applicable. These are not ducts serving a Type II hood (506.4). The exhaust equipment is serving a Type I hood, so those applicable sections would apply. Other applicable sections: 507.4, 507.6, 507.1.1, 507.9, 507.10, 507.11, 507.12, and 507.13. Section 509 is the only place where it begins to be grey. Might as well just throw the suppression system in, and you would have a fully functional Type I hood.
No problemSifu said:As it stands now (it is a moving target right now) the tenant wants to put in light duty appliances but has purchased a used type I hood and wants to use it as a type II hood without suppression or grease filters and ducts. I understand you can install a type I where a type II is required but it is a little grey as to whether all the requirements for a type I ( filters, suppression, ducts, clearances etc) would apply. I think it is ok except for a potential listing problem. This is not one of my projects, another inspector and plan reviewer have asked me and I (I guess none of us) have never encountered the question before. Thought I would put it out here to see what others think.
Yes and no........clear as mud said:IMC 102.8 Hood listing supercedes code.
clear as mud!!!clear as mud said:Sorry. ...unless the code is more restrictive.304.2
Looking at 506,7,8,9. Wondering if 507.1 is poorly written or written correctly ???New in the 2015 IMC' date=' note the last section of the section: 507.1 General. Commercial kitchen exhaust hoods shall comply with the requirements of this section. Hoods shall be Type I or II and shall be designed to capture and confine cooking vapors and residues. A Type I or Type II hood shall
be installed at or above all commercial cooking appliances in accordance with Sections 507.2 and 507.3. Where any cooking
appliance under a single hood requires a Type I hood, a Type I hood shall be installed. Where a Type II hood is
required, a Type I or Type II hood shall be installed. Where a Type I hood is installed, the installation of the entire system,
including the hood, ducts, exhaust equipment and makeup air system shall comply with the requirements of Sections 506,
507, 508 and 509.
No cda, I'd call that clarification.New in the 2015 IMC' date=' note the last section of the section: 507.1 General. Commercial kitchen exhaust hoods shall comply with the requirements of this section. Hoods shall beType I or II and shall be designed to capture and confine cooking vapors and residues. A Type I or Type II hood shall
be installed at or above all commercial cooking appliances in accordance with Sections 507.2 and 507.3. Where any cooking
appliance under a single hood requires a Type I hood, a Type I hood shall be installed. Where a Type II hood is
required, a Type I or Type II hood shall be installed. Where a Type I hood is installed, the installation of the entire system,
including the hood, ducts, exhaust equipment and makeup air system shall comply with the requirements of Sections 506,
507, 508 and 509.
Where is the requirement that the hood has to be listed?....I am with MT, The grease filters and duct and suppression are what make it a Type I hood, if it is "fabricated like" a Type I it would meet a IIIMC 102.8 Hood listing supercedes code.
- greaseThis is a great thread, thank you all, the comments have been super helpful. I think this is sort of related to our specific puzzle to solve. We've been looking close at Type 1 vs Type 2 hood requirements supporting panini grills and sandwich steamers. It appears that way back in the day (about twenty years ago) panini grills got popular at Panera and similar places, and were often out in the open on a counter and perhaps under Type 2 as extra vs minimum required. Fast forward to present, it appears due to (refreshed) fire code and mechanical code and health code details pretty much specify heat and moisture criteria for Type 2 - anything with potential smoke or miscible great goes right to Type 1 (albeit fire suppression not needed for panini grills). It look to me like ventilation and exhaust grey areas or gaps closed around panini grills. To solve the "small appliance" use case, it appears lighter duty Type 1 vent hood equipment with appropriate NFPA and UL and NSF certs fit this middle ground use case for panini grills can be purchased. This lighter duty Type 1 would include the customary grease filters but not be rated for deep frying use case. Sound about right? Thanks again!