I am designing a commercial post frame (pole barn) building in Wisconsin, climate Zone 6a. Wall construction is as follows:
3-ply 2x8 embedded columns at 8 ft o.c., R19 batt insulation, 2x6 wall girts on exterior face, 26 gauge exterior ribbed steel, 4-mil poly vapor barrier, 2x4 girts on inside face, 29 gauge interior liner panels.
I am familiarizing myself with the energy code requirements of these buildings, and working on envelope calculations using COMcheck. I am summing up the R-values of the wall components and determining the U-factor. I understand the ribbed steel and liner panels do not provide any insulation value.
Is it reasonable to consider: 19 (batt insulation) + 0.83 (4-mil poly) + 1.0 (1.5" air space from the 2x4 wall girts on the inside face) = 20.83. Therefore, U = 1/20.83 = 0.048. Is this an acceptable calculation? By comparison, a wood frame wall with studs at 24" o.c. and R19 cavity insulation yields a U-factor of 0.065. Perhaps I should increase to R25 batt insulation, given that the wall cavity is 8".
Any input or feedback is appreciated. Researching online, I have not found much on the topic of energy U-factors for post frame building walls.
-Troy
3-ply 2x8 embedded columns at 8 ft o.c., R19 batt insulation, 2x6 wall girts on exterior face, 26 gauge exterior ribbed steel, 4-mil poly vapor barrier, 2x4 girts on inside face, 29 gauge interior liner panels.
I am familiarizing myself with the energy code requirements of these buildings, and working on envelope calculations using COMcheck. I am summing up the R-values of the wall components and determining the U-factor. I understand the ribbed steel and liner panels do not provide any insulation value.
Is it reasonable to consider: 19 (batt insulation) + 0.83 (4-mil poly) + 1.0 (1.5" air space from the 2x4 wall girts on the inside face) = 20.83. Therefore, U = 1/20.83 = 0.048. Is this an acceptable calculation? By comparison, a wood frame wall with studs at 24" o.c. and R19 cavity insulation yields a U-factor of 0.065. Perhaps I should increase to R25 batt insulation, given that the wall cavity is 8".
Any input or feedback is appreciated. Researching online, I have not found much on the topic of energy U-factors for post frame building walls.
-Troy