So, I have an unlimited area building of B/F use. About 200,000 sq. ft. Fully sprinklered. 60 foot clear around except for a very limited area that is only 40 feet. Now they want to bring in a pre-manufactured "enclosure" that will be 65 feet long by 24 feet wide by 11 feet tall. It houses air compressors. There are four roof top HVAC units on top so it becomes 15 feet tall. There are two doors, one at each end. It is set 18 inches away from the actual principle unlimited area building Shutters along the front side. This "enclosure" to me seems to fit the definition of building or structure according to the IBC. They want to call it "equipment" or an "appliance".
I said to build it as an addition and apply all applicable codes, including sprinklers or move it 40 feet away.
Thoughts?