Mech
2009 IPC
I have a building without any soil or waste stacks. There are several fixtures being vented on a branch vent. Where the branch turns vertical and passes through the roof, is this portion still sized as a branch vent (Section 916.2) or is it sized as a vent stack (Section 916.1 and Table 916.1), using the building drain size as the soil / waste stack size?
916.2 Vents other than stack vents or vent stacks. The diameter of individual vents, branch vents, circuit vents and relief vents shall be at least one-half the required diameter of the drain served. The required size of the drain shall be determined in accordance with Table 710.1 (2). Vent pipes shall not be less than 11/ 4 inches (32 mm) in diameter. Vents exceeding 40 feet (12 192 mm) in developed length shall be increased by one nominal pipe size for the entire developed length of the vent pipe. Relief vents for soil and waste stacks in buildings having more than 10 branch intervals shall be sized in accordance with Section 914.2.
916.1 Size of stack vents and vent stacks. The minimum required diameter of stack vents and vent stacks shall be determined from the developed length and the total of drainage fixture units connected thereto in accordance with Table 916.1, but in no case shall the diameter be less than one-half the diameter of the drain served or less than 11/ 4 inches (32 mm).
Thanks.
Thanks.