What determine the amount of accessibility?

error404

Bronze Member
Joined
Jun 10, 2013
Messages
49
Location
United States
Use Group: A-2

IBC 2003,NFPA 2006, ANSI A117.1 2003

1 Story Existing Restaurant with an outdoor deck /lounge area (intended to serve food).

Scope of work: extend deck area (not fixed seating) (12' x 21')

Client wants the new concrete deck to have a 6" step, so the new addition will not be accessible.

Me being more of a residential type of architect, I was wondering what determine the amount of accessibility required?

All I can find was from IBC:

1108.2.9 Dining areas. In dining areas, the total floor area

allotted for seating and tables shall be accessible.

thanks a lot!
 
Your under IBC 2003?. It is very easy to make a 6" elevation change accessible. More than likely you would only need to make 5% of each type of seating accessible, but if this new raised area provides any different type of experience, seating option, view, or amenities then the area itself will need to be accessible.
 
JPohling said:
Your under IBC 2003?. It is very easy to make a 6" elevation change accessible. More than likely you would only need to make 5% of each type of seating accessible, but if this new raised area provides any different type of experience, seating option, view, or amenities then the area itself will need to be accessible.
Thanks a lot for the response...

I see where it says:

1108.2.9.1 Dining surfaces. Where dining surfaces for

the consumption of food or drink are provided, at least 5

percent, but not less than one, of the seating and standing

spaces at the dining surfaces shall be accessible and be

distributed throughout the facility.

But, 1108.2.9 says:

1108.2.9 Dining areas. In dining areas, the total floor area

allotted for seating and tables shall be accessible.

So, I figure the whole dining area needed to be accessible and in that area at least 5% needed to comply with ANSI A117.1 902 (Dining Surfaces and Work Surfaces)

Am I misunderstanding it?

thanks!
 
Looks like you got it....Don't forget Chapter 34 or IEBC for alterations and additions and stuff....

error404 said:
Thanks a lot for the response...I see where it says:

1108.2.9.1 Dining surfaces. Where dining surfaces for

the consumption of food or drink are provided, at least 5

percent, but not less than one, of the seating and standing

spaces at the dining surfaces shall be accessible and be

distributed throughout the facility.

But, 1108.2.9 says:

1108.2.9 Dining areas. In dining areas, the total floor area

allotted for seating and tables shall be accessible.

So, I figure the whole dining area needed to be accessible and in that area at least 5% needed to comply with ANSI A117.1 902 (Dining Surfaces and Work Surfaces)

Am I misunderstanding it?

thanks!
 
This is a new space, it needs to be accessible. "....and be distributed throughout the facility. provide a ramp, or lower it.
 
There is an exception in the ADASAD for addition s and remodels that the raised "platform" in restaurants do not need to be accessible, but many states require the platform to be accessible.
 
mark handler said:
There is an exception in the ADASAD for addition s and remodels that the raised "platform" in restaurants do not need to be accessible, but many states require the platform to be accessible.
I should have clarified... it's a 6" step down. The step is there for no other reason than aesthetics (and create a tripping hazard).
 
ADASAD 206.2.5 Restaurants and Cafeterias. In restaurants and cafeterias, an accessible route shall be provided to all dining areas, including raised or sunken dining areas, and outdoor dining areas.

EXCEPTIONS: 2 In alterations, an accessible route shall not be required to existing raised or sunken dining areas, or to all parts of existing outdoor dining areas where the same services and decor are provided in an accessible space usable by the public and not restricted to use by people with disabilities.

Advisory 206.2.5 Restaurants and Cafeterias Exception 2. Examples of "same services" include, but are not limited to, bar service, rooms having smoking and non-smoking sections, lotto and other table games, carry-out, and buffet service. Examples of "same decor" include, but are not limited to, seating at or near windows and railings with views, areas designed with a certain theme, party and banquet rooms, and rooms where entertainment is provided
 
mark handler said:
ADASAD 206.2.5 Restaurants and Cafeterias. In restaurants and cafeterias, an accessible route shall be provided to all dining areas, including raised or sunken dining areas, and outdoor dining areas.EXCEPTIONS: 2 In alterations, an accessible route shall not be required to existing raised or sunken dining areas, or to all parts of existing outdoor dining areas where the same services and decor are provided in an accessible space usable by the public and not restricted to use by people with disabilities.

Advisory 206.2.5 Restaurants and Cafeterias Exception 2. Examples of "same services" include, but are not limited to, bar service, rooms having smoking and non-smoking sections, lotto and other table games, carry-out, and buffet service. Examples of "same decor" include, but are not limited to, seating at or near windows and railings with views, areas designed with a certain theme, party and banquet rooms, and rooms where entertainment is provided
Thanks Mark, I found the section that you are referring on my copy of 2010 ADASAD... (My county is on 2003 ANSI though). I'll look for the exception on ANSI...

I appreciated your time & help!
 