Mr. Inspector
SAWHORSE
I'm trying to find a way out for a friend that is installing a wood stove in a sunroom so the sunroom does need to have or upgrade insulation as the local inspector is requiring. Sunroom is finished and the existing if any insulation is unknown.
2015 IECC under existing buildings
The sunroom code book let's you use the IECC)
R503.2 Change in space conditioning. Any nonconditioned
or low-energy space that is altered to become conditioned
space shall be required to be brought into full compliance
with this code.
Exception: Where the simulated performance option in
Section R405 is used to comply with this section, the
annual energy cost of the proposed design is permitted to
be 110 percent of the annual energy cost otherwise
allowed by Section R405.3.
I was thinking he could say he had a portable heater in the sunroom and it is not being changed from a nonconditioned to a conditioned space. Would you accept that?
Or how would you prove that the sunroom would meet this exception? Would the existing wall between the house and the sunroom need to be brought up to the 2015 code?
2015 IRC 1102.1.Exceptions
The following low energy buildings or portions thereof, separated from the remainder of the building
by building thermal envelope assemblies complying with
this section shall be exempt from the building thermal
envelope provisions of Section N1102.
1. Those with a peak design rate of energy usage less
than 3.4 Btu/h · ft2 (10.7 W/m2) or 1.0 watt/ft2 of
floor area for space conditioning purposes.
2. Those that do not contain conditioned space.
Also if someone put a wood stove or fireplace on a patio would you require them to build a insulated room around it?
2015 IECC under existing buildings

R503.2 Change in space conditioning. Any nonconditioned
or low-energy space that is altered to become conditioned
space shall be required to be brought into full compliance
with this code.
Exception: Where the simulated performance option in
Section R405 is used to comply with this section, the
annual energy cost of the proposed design is permitted to
be 110 percent of the annual energy cost otherwise
allowed by Section R405.3.
I was thinking he could say he had a portable heater in the sunroom and it is not being changed from a nonconditioned to a conditioned space. Would you accept that?
Or how would you prove that the sunroom would meet this exception? Would the existing wall between the house and the sunroom need to be brought up to the 2015 code?
2015 IRC 1102.1.Exceptions
The following low energy buildings or portions thereof, separated from the remainder of the building
by building thermal envelope assemblies complying with
this section shall be exempt from the building thermal
envelope provisions of Section N1102.
1. Those with a peak design rate of energy usage less
than 3.4 Btu/h · ft2 (10.7 W/m2) or 1.0 watt/ft2 of
floor area for space conditioning purposes.
2. Those that do not contain conditioned space.
Also if someone put a wood stove or fireplace on a patio would you require them to build a insulated room around it?