With gas lines and electric involved, I would assume that the permitting office knows it's an outside application?
Did they just get the wrong tank-less WH?
 
Photovoltaic array on a roof:

31728137457_08ea415f1e_b.jpg

39704840543_b700fab4c5_b.jpg

45754760345_95f58ba010_b.jpg


This picture is from today. You know, I don't walk on tile roofs, steep roofs, high roofs, so I don't see the inside of a lot of junction boxes except for a picture. I can't tell if a c-tap has been installed correctly from a picture....I can't pulll the c-tap off the wires and put it in my pocket. I have quite a collection.

I have come to the conclusion that even if the correct size c-tap is installed with the correct crimp tool, I will still be able to remove the c-tap with my bare hands. That hardly qualifies as an irreversible connection as is required by code.

I'm telling you that these c-taps are junk. I have had them fall off without me touching them and too many inspectors are not aware of the problem and some do not bother to look.
 
Last edited:
I went to the wrong house today. The inspection was for an electrical service upgrade. I noticed this while I was waiting for someone to answer the door. The lady said that they didn't get a new el service and by the way, you're at the wrong house. So I gave her a correction slip and off I went.

45957536714_91c5c3481e_b.jpg

45957535074_7a940864cb_b.jpg
 
This was first inspected on 12-19-18. It is now 1-9-19 and nothing has changed. At the first inspection it was just me and the owner. I made it clear to him that he must get the contractor to fix this. The cabinet is mounted over a hole and I left correction to start over and do not leave exposed energized metal. The electrician was there today....I fired him.

45767181865_a8f63d2584_b.jpg

45957534034_69076755bb_b.jpg


45957533704_eedffc630d_c.jpg
 
Last edited:
MC with a bonding jumper, haven't seen that one, is that the GC?

Never seen the Hots coiled like that, you okay with that?
 
I asked him why the tape was there. He apologized for not doing it correctly. He said that he has more tape and can fix this while we wait. I asked him again why the tape is there. He said that was to separate the clamp from the armor because of dissimilar metal corrosion.

45780129595_4bd296bdeb_c.jpg

He is a genuine electrical contractor that has been at it for more than a few years. He assured me that he has done this hundreds of times and never has anyone asked the question. I believe him....
 
Last edited:
The job is an patio cover. The correction stated "Bond the metal that is within five feet of the water's edge." The guy that met me was happy to see me. He does clean work. A tad bit wrong but clean. He's as old as I am and we taught each other few things today. I like when that happens.

45970928984_af341befe9_b.jpg

45780347615_1c22e532d4_b.jpg

39730652193_62393b1280_z.jpg

The paint interrupts the bond. The clamp could be below the level of the concrete.
 
Last edited: