If an electrician fails a final inspection because the dishwasher is not AFCI/GFCI protected as per the 2014 NEC, can he buy a combo AFCI/GFCI receptacle and install it and be compliant?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Possibly....New circuit or existing?
Maybe...maybe not. If the branch circuit wiring is in a raceway up to the receptacle outlet, an AFCI receptacle would be permitted.
2014NEC, 210.8 (d) requires GFCI's for dishwashers
2014NEC, 210.12 (a) requires AFCI's
I would say yes as the AHJ.
2014NEC, 90.4 Enforcement. allows new products or materials that may not have been ready at time of adoption. If the electrician meets the code using the combo versus the breaker he is meeting the intent of the code for safety and I would allow the combo's use.