Would the Panelboard bonding described on 517.14 have to be in a conduit from panelboard to other panelboards?
would 300.3 (2) apply?
would 300.3 (2) apply?
Last edited:
1) Nothing requires the #10 bond to be in conduit, however, if it was in a metallic conduit, 517.19(E) would apply.Would the Panelboard bonding described on 517.14 have to be in a conduit from panelboard to other panelboards?
would 300.3 (2) apply?
JAR546 please reread 300.3(2) because it says "Grounding and bonding conductors" BTW I am referring to NFPA 70 2017 version. the panels are not all in the same room (or same floor)
the contractor ran conduit between location but once inside the electrical room stopped using conduit. It is not yet complete.
can you explain to me where the 1000V comes into play? I do not see where the voltage is stated under 517
300.3 (B) (2)