klarenbeek
Its about 800 pounds plus associated duct.  Up here we also have to deal with thing like snow load also....
It’s surprising that the contractor would risk that without an assurance that the structure could withstand that. You should consider a red tag for the restaurant.Its about 800 pounds plus associated duct. Up here we also have to deal with thing like snow load also....
Same requirements here. A lot of older buildings were designed with a 35 PSF roof snow load because the heat loss through the roof would help melt the snow throughout the winter. Today it is a 47 PSF roof snow load (not ground). So, if you are adding insulation when re-roofing an existing building or replace roof top equipment an engineer needs to verify the existing structure will support the increased snow loads, including snow drifting for the equipment being installed.Real situation I currently have: Mechanical contractor added (not replaced) a rooftop unit to an existing restaurant, no other work being done. I have a correction for needing structural analysis by a structural engineer to make sure the roof can support the extra weight. My entire professional background is HVAC, so I'll be the first to admit I'm not qualified for that analysis. That's why I'm asking for it. What other means would I have to ensure code compliance?
My point is that in post #117 you used the word "guarantee". That is a much higher standard of liability than "ordinary standard of care".But this does not stop building departments from trying to impose liability on engineers and architects. This is often done by forms the design professional is expected to sign. The building department should focus on code compliance, not on who should be responsible.
Most building departments do both. Asking an engineer to answer a question in writing makes an engineer responsible for that answer. How could it be otherwise?
Comparing the work to an engineer’s structural observation report indicates that many engineers aren’t all that concerned about responsibility .
Most interactions that I have with engineers are related to clarifying the engineer’s details and instructions. Understand that not all engineers are created equal. Some do a great job and with some it’s hard to tell what they were attempting. In as much as engineers rarely deal with code, hardly ever know the code and look forward to billing for their time, I have no compunctions asking for an engineer to weigh in.I am fine with answering a question in writing as long as (1) the questioner cites a specific code reference, and (2) the questioner indicates what they believe to be the observed deviation from the referenced code.
That’s where I probably disagree with your approach, assuming I understand it correctly, and you were acting as the inspector (not the plan checker).I’ve upset engineers by telling the contractor that the design was too weak… go back for more.
When the day comes that we can hook them up to one of Elon’s Neural Links… perhaps then I could force them to think. When it comes to beams, my comment, if there is one, is in the other direction. If the floor flexes that might get a reaction.probably not within your purview to force them to think about how they will build it
By asking for verification that that the structure can support the added weight you are addressing a code issue..Real situation I currently have: Mechanical contractor added (not replaced) a rooftop unit to an existing restaurant, no other work being done. I have a correction for needing structural analysis by a structural engineer to make sure the roof can support the extra weight. My entire professional background is HVAC, so I'll be the first to admit I'm not qualified for that analysis. That's why I'm asking for it. What other means would I have to ensure code compliance?
There is a point in the process where we are acting as a mitigator of liability. We have a common-law duty of care to reduce liability and risk for both our employer (the municipality/AHJ) and the client.I can always follow your rules, and by your rules I mean society’s rules, well then, by your rules I should have watched the contractor pump grout under a slab and let him and the engineer figure it out for themselves. The professional approach gums up the works. Trust me on this, the victims of my overreach like the time frame.
Can you provide cases law indicating that a building department has been held liable for not performing a peer review on an engineer's calculations?The responsibility of an engineer is defined by case law and a number of state statutes. Thus there is no need for the building department to try to hold the engineer responsible. This is why a building department should have an engineer either on staff or on contract. A building department that does not have somebody qualified to check the calculations and believes that they have fulfilled their responsibility by requiring an engineer sign the submittal is not doing their job.
And the psf weight at the support....?What is the weight of the equipment?
Same here...unless the building is "newer"...Same requirements here. A lot of older buildings were designed with a 35 PSF roof snow load because the heat loss through the roof would help melt the snow throughout the winter. Today it is a 47 PSF roof snow load (not ground). So, if you are adding insulation when re-roofing an existing building or replace roof top equipment an engineer needs to verify the existing structure will support the increased snow loads, including snow drifting for the equipment being installed.
When you had this conversation with the owner/builder, was this just given as friendly advice?When the day comes that we can hook them up to one of Elon’s Neural Links… perhaps then I could force them to think. When it comes to beams, my comment, if there is one, is in the other direction. If the floor flexes that might get a reaction.
Here is an example: The job was a truck dock canopy. Huge it was and held to the building with joist hangers. I was standing there with the owner/builder. I mentioned that HDs and all-thread every eight feet would be a nice touch. Well excuse me but it was weak. I never heard from the upset engineer… but I heard that he was upset.
The HDs went into the building but not the plans. He took it next level with doubled joists inside the building and out, There was blocking and CS16. I could have talked him into 3/4” roof sheathing. I wasn’t weak after that.
You did catch the part when I said that some engineers are sketchy? I’ve run into all manner of mistake and value engineered structures that lost all of the value. Following a formal procedure as you suggest functions in the professional settings of your workday… not a large helping of professional in mine.
I had a good relationship with the owner. The facility was larger than one would expect for a company that distressed blue jeans by the truckload. There were rows of washing machines that were big enough for a Shetland pony. He was a licensed B contractor that specialized in setting up mobile home parks.... so he had construction experience... but I had more. His daughters owned the blue jean business and the Fire Marshall scared them. They insisted that I be there whenever the loony FM showed up.When you had this conversation with the owner/builder, was this just given as friendly advice?
Or, acting in the role of inspector for the AHJ, did you state or imply that you would refuse to sign off on the structure built according to approved, engineered plans unless the owner/builder added more structural components of your own design?
There is a difference in how you handle a lender asking for something to be certified and a building official refusing to issue a certificate of occupancy until the engineer certifies the project.My point is that in post #117 you used the word "guarantee". That is a much higher standard of liability than "ordinary standard of care".
I have often had lenders and funders ask me to "certify" in writing that the (California) building that I had designed in meets "all codes and regulations". One lender pushed back when I said they needed to be more specific, so I asked them if it needed to comply with the Code of Hammurabi.
I've had others want me to certify that the entire apartment project meets ADA. I point out to them that ADA includes not just physical design requirements but also deals with nondiscrimination in leasing, over which an architect has no control. The legal definition of "certify" in the California BPC limits certifications to an ordinary standard of care exercised by an architect.
That came from the engineers. Greed caused them to invent the structural observation.building official refusing to issue a certificate of occupancy until the engineer certifies the project.
You say that.In those relatively rare situations where an engineer has made a mistake
You know, there's all kinds of engineers, civil, electrical, mechanical, soils. Are the building departments not allowed to trust any engineer? Can't they save a buck and roll the dice that the engineers so seldom blow it that the cost outweighs the benefit?A building department that does not have somebody qualified to check the calculations and believes that they have fulfilled their responsibility by requiring an engineer sign the submittal is not doing their job.
....in that situation, IMO that's when you should go back to the plan checker and have him justify his previous approval, before you "refuse to accept".I have refused to accept what the engineers have said was good enough.... more than once and less than I should have
I would argue that spring hinges are a "closer".....If it's just friendly advice, then good for you, and you may have been of great benefit to the Owner.
But when you say...
Because once the project is under permit, the AHJ has ALREADY ACCEPTED what the engineers said, and now the burden of proof is on you as inspector to demonstrate, using your own code analysis or that of the plan checker, why that previous AHJ approval should be withdrawn.
Yes, you have to "follow the rules that govern society". the rules that govern and limit your authority; otherwise you are Ultra Vires.
My turn to provide an example:
I had an inspector force a contractor to move a wall adjacent to an entry door over almost a foot in an ADA mobility unit to get strike clearance on the push side of the entry door. The contractor, not wanting to delay the project, did as the inspector ordered. No correction was issued, so I as DPOR was not made aware of it until it was too late. I assume the inspector thought he did the owner a big favor.
The contractor then sent the owner a change order saying it was a code deficiency. Now the Owner is spending more money and thinks it's my fault, so they call me and ask how I could have missed this. I show the owner on the plans how this door had spring hinges, not a closer, so the 12" push side clearance was not required by code. Even worse, moving the wall per the inspector's demands shrunk down the adjacent kitchen, so that the storage shelving no longer met the 50% accessible requirement in ADA. It all had to be reframed back to where it was originally, causing delay and yet another expense... as well as a lot of my time just to prove my approved plans were already code compliant.
If the inspector had followed "the rules of society" and written a correction with the applicable code citation, I could have quickly responded/refuted it; or better yet, the inspector would have first been forced to look more closely at the approved plans and the code, and realized that there was no code violation / no correction was required in the first place.
Where can I get that on a hat?Ultra Vires
In CBC 11B and ADA, a "spring hinge" (404.2.8.2) is not the same thing as a "closer" (404.2.8.1).I would argue that spring hinges are a "closer".....
I assume you are talking about closing speed, and even though they are treated differently there, they both close the door and IMO require the better maneuvering...Unless spring hinges exert that much less force and can be quantified somehow..In CBC 11B and ADA, a "spring hinge" (404.2.8.2) is not the same thing as a "closer" (404.2.8.1).